Lightbulb AC condenser fan shuts off

I had the outside fan shutting off or not starting , when it did run would last couple of minutes, compressor runs fine. If I give the fan blade some momentum it will run for a minute then shut down. I had an extra motor and installed that motor and have the same problem, could it be something else or just bad luck with 2 motors. I am afraid to buy a new one and wonder if the same thing will happen? any other causes??
 
  #2  
Old 05-23-13, 02:57 PM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,498
Received 1 Vote on 1 Post
Sounds like a capacitor issue..
 
  #3  
Old 05-23-13, 04:19 PM
R
Member
Thread Starter
Join Date: May 2013
Location: United States
Posts: 12
Received 0 Votes on 0 Posts
I have 3 capacitors and have tried each with the same result. When I started the motor with no blade it would run more often than not so I thought the same that the fan was not getting juiced enough, none were new though so I may try another . thank you
 
  #4  
Old 05-23-13, 04:24 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,244
Received 2 Votes on 2 Posts
whenever you install a new motor you must also install the correct capacitor for the new motor.
 
  #5  
Old 05-23-13, 08:21 PM
R
Member
Thread Starter
Join Date: May 2013
Location: United States
Posts: 12
Received 0 Votes on 0 Posts
thanks for help

The one I put in was a working unit w cap so I assumed it would work. I am going to buy a new one tomorrow 5mfd 370vac oval run capacitor The fan I purchased is
Fasco D727 5.6-Inch Direct Drive Blower Motor, 1/3 HP, 115 Volts, 1075 RPM, 3 Speed, 5.9 Amps, OAO Enclosure, Reversible Rotation, Sleeve Bearing
 
  #6  
Old 05-24-13, 01:46 AM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,244
Received 2 Votes on 2 Posts
The outdoor init is 240v! Not 115v!
 
  #7  
Old 05-24-13, 11:19 AM
R
Member
Thread Starter
Join Date: May 2013
Location: United States
Posts: 12
Received 0 Votes on 0 Posts
The motor that was in the system working for the past 5 years is 115v, the pull from another system in the building is 115v, this is a YORK heat pump dated about 1980, I will try to check another unit but 115v are all I have seen.
 
  #8  
Old 05-24-13, 04:06 PM
R
Member
Thread Starter
Join Date: May 2013
Location: United States
Posts: 12
Received 0 Votes on 0 Posts
I put in the new motor and capacitor

When I turn the system I can see a large spark in the motor as it starts, it runs fine for 60 seconds +- then another large spark and it stops. This is with 2 motors. Please tell me what could cause this? thank you
 
  #9  
Old 05-24-13, 04:43 PM
T
Member
Join Date: Jun 2012
Posts: 1,012
Received 19 Votes on 15 Posts
Your using the wrong motor, the condenser is 240 volts.
 
  #10  
Old 05-24-13, 06:50 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,244
Received 2 Votes on 2 Posts
There should be a data plate on the unit... verify the voltage!
 
  #11  
Old 05-24-13, 08:08 PM
R
Member
Thread Starter
Join Date: May 2013
Location: United States
Posts: 12
Received 0 Votes on 0 Posts
There were 3 different capacitors strapped into the unit I suppose other repairers did not take them out, they all were 5/370 or 7.5 370 units. I have the wiring diagram but I cant tell much from it. The first motor that started the issue has hardly any ID left on it. I can see 60 on it thats all. I guess no matter what I thought I saw the fact that all are 220 proves the motor was a 220.
 
  #12  
Old 05-25-13, 07:34 AM
T
Member
Join Date: Jun 2012
Posts: 1,012
Received 19 Votes on 15 Posts
Yes, 220 - 240, not 115! You will blow a 115 motor with 220 - 240 volts (sparks) which is what happened to you.
 
 