Is it capacity?

Reply

  #1  
Old 08-31-13, 09:26 PM
Member
Thread Starter
Join Date: Aug 2010
Location: usa
Posts: 223
Is it capacity?

I have rental house (Texas Dallas area) of 1700 sqft. The AC is 3 ton and 10 years old. The ceiling is medium in height.

It seems for the hottest days, the temp can't drop below 80 degrees. Last year, there were a couple of days. At that time, I had an AC tech check it out and everything was OK.

Today (highest reached 106 degrees), tenant said that the temp couldn't drop below 80 degrees.

I begin to wonder if the AC is just undersized for a few hottest days in the summer rather than AC issues?

anyone else has similar experience?
 
Sponsored Links
  #2  
Old 09-01-13, 01:49 AM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,471
Upvotes Received: 16
A 3 ton unit should be adequate for that size house IF the house has decent insulation, a ventilated attic, the duct work is of adequate size AND insulated, the house is reasonably air tight and the tenant is not trying to cool the great outdoors by also having a door or windows open.

That is a lot of ifs for you to check out. Add in holes in the duct work allowing cooled air to escape or hot air to enter.
 
  #3  
Old 09-02-13, 07:40 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 715
I agree with Furd; that would be a drop of 26F, at or below 50% RH & 80F with air movement using ceiling fans or floor type fans - will keep occupants comfortable.
 