Ac: smaller cooper line sweating


  #1  
Old 09-15-13, 04:19 AM
B
Member
Thread Starter
Join Date: Sep 2013
Location: usa
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ac: smaller cooper line sweating

I have an older condenser but mechanically everything's working fine. My ac blows almost room temp air and the smaller of the two cooper lines is very cold to the touch and sweating. The larger cooper line is a little above room temp. My ac guy has changed the orface and has cut the copper lines in several spots to blow them out with nitrogen to see if there was a clog. The system is charged with r22 and has been checked several times to see if its over or under. Any help would be greatly appreciated. First time home buyer and am going nuts with this one!
 
  #2  
Old 09-15-13, 04:34 AM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,646
Received 82 Upvotes on 72 Posts
Have you checked to see if the evaporator coil is freezing up? How is the airflow, is it weak? If so, that's often an indication that the evaporator is freezing up.
 
  #3  
Old 09-15-13, 05:00 AM
B
Member
Thread Starter
Join Date: Sep 2013
Location: usa
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yeah both coil a-coil and condenser coils have been cleaned thoroughly
 
  #4  
Old 09-15-13, 06:08 AM
T
Member
Join Date: Jun 2012
Posts: 955
Received 31 Upvotes on 25 Posts
The first issue I see is how could the tech possibly verify the charge if the system is indeed operating like that? It's basically impossible.

Is this a heat pump?
 
  #5  
Old 09-15-13, 09:51 AM
B
Member
Thread Starter
Join Date: Sep 2013
Location: usa
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
The system is a split system cooling by trane. The first time the coolant was check was about a 6 weeks ago and ot was fine this is before I had the problem was just getting it checked since I just got the house. Since I've had the problem it was rechecked and it was sitting at the same.
 
  #6  
Old 09-15-13, 11:15 AM
T
Member
Join Date: Jun 2012
Posts: 955
Received 31 Upvotes on 25 Posts
Doesn't sound rite.
If the system isn't cooling and the line set temperatures are all wrong, then there's no way a tech could measure the systems refrigerant level. It's just not happening.
I think you might need to look for a new HVAC company.
 
  #7  
Old 09-22-13, 08:49 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
It would appear there could be a restriction, somewhere upstream, in the small high-side liquid line going to the metering device to the evaporator coil; perhaps a partially plugged liquid-line filter/drier.

This will cause a pressure drop & vaporization of some of the liquid in the line, this will lead to condensation, &/or frosting of the line.

You can't check the charge when there is a restriction in the flow of refrigerant...it won't be accurate in any way...superheat & subcooling will both be high; head pressure, suction & compressor amp-draw will all be low.
 
 