air works but heat not blowing through the vents.

I have been using my central heat - a/c all summer for cold air and it was working fine. It is now getting cold so we switched it to heat and it is on and runniing but no air is blowing out of the vents.
 
  #2  
Old 10-17-13, 05:39 AM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,646
Received 82 Upvotes on 72 Posts
To summarize, your air handler (blower) isn't turning on when the thermostat calls for heat, but it does when the thermostat calls for cooling? If so, check to see if you have 24VAC at the G terminal on your thermostat (with the thermostat calling for heat). Alternatively, you can temporarily jumper the G terminal to the R or RH terminal on the thermostat. If the blower turns on, your thermostat is likely defective.
 
  #3  
Old 10-18-13, 10:20 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
It's possible it could also be a furnace with a fan switch that senses the plenum temperature & only cycles the fan when that temp is finally reached.

Did you wait long enough?
 
 