AC condenser will not turn on
Old 10-23-13, 09:36 PM
I have a carrier condenser I have replaced the capacitor and the contactor is good I get voltage on both sides when I turn on my ac unit. but my compressor and fan do not turn on. what can be the problem?
Old 10-23-13, 11:59 PM
Received 3,897 Upvotes on 3,494 Posts
Welcome to the forums.
It would not be likely that the compressor and fan are both bad which means that you have a power problem.
You need to confirm that the contactor is actually engaged. You need to check for 240 VAC on both sides of the contactor. Not 120vac to ground.....
Name:  contactor check.jpg
Old 10-24-13, 07:04 PM
thank you, you were right it was a power problem. my breaker was bad one leg was burnt. thanks again
Old 10-24-13, 07:19 PM
Your welcome and thanks for leaving us an update