Fan stopped spinning and at a brick wall

I bought a replacement motor, starter cap, and still when the AC is turn on, the fan doesn't spin. Cold air is coming into the house but not much. I checked the voltage coming from the thermostat and it shows 24V. The energized switch is closing when ac is on and I measured 120V from chassis to both Line terminals. It is an airflow system and I'm lost. Any thoughts or ideas are appreciated.
 
  #2  
Old 10-25-13, 08:52 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,108
Received 3,986 Upvotes on 3,578 Posts
Welcome to the forums.

Check the wiring where it connects to the control box inside the furnace/air handler....... look for terminal G. It should have a green wire on it. Try touching a jumper wire from the G terminal to the R terminal and see if that starts the fan. If you have the blower door off you will need to hold the safety switch in.

If the blower starts you have a thermostat problem or the wiring going to it.
 
  #3  
Old 10-26-13, 06:37 PM
T
Member
Thread Starter
Join Date: Oct 2013
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Problem solved. One of the 30A fuses was blown. There was so much paint covering the box that it was difficult to open.
 
 