Lennox Elite Condenser will not turn on call for cool


  #1  
Old 05-13-14, 07:00 PM
K
Member
Thread Starter
Join Date: Dec 2011
Location: USA
Posts: 30
Likes: 0
Received 0 Likes on 0 Posts
Lennox Elite Condenser will not turn on call for cool

My AC outside unit is not working. Here is what I tested:

(1) On the outside unit I do not get 24v across the contactor. When I manually press the contactor the unit is working.
(2) On the control board (surelight), I do not get 24v on Y and C when call for cool. I think I should get 24v, shouldn't I?
(3) The (indoor unit) blower fan works when call for cool.

What else can I check? Is this a bad compressor relay on the control board?

Thanks!!!
 

Last edited by katgoo; 05-13-14 at 07:15 PM.
  #2  
Old 05-13-14, 07:07 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,007
Received 3,181 Likes on 2,856 Posts
On the control board (surelight), I do not get 24v on Y and C when call for A/C
The thermostat is where the Y wire gets its 24vac from. You have a thermostat problem or break in the Y wire. You can try connecting Y to R at thermostat to see if the compressor comes on.
 
  #3  
Old 05-14-14, 06:41 AM
K
Member
Thread Starter
Join Date: Dec 2011
Location: USA
Posts: 30
Likes: 0
Received 0 Likes on 0 Posts
PJMax - you are the best! MANY thanks. I misread a wiring diagram...

It was a disconnected thermostat wire at the control board terminal: the exposed part was still connected but the rest of the wire was hiding from me when I first looked :-)

Easy fix. Thanks again. This board is awesome!
 
 