No power to thermostat

My thermostat is not getting power. I am attempting to locate and replace the 3 amp fuse at the air handler but cannot find it. Attached is a photo of the circuit board at the air handler (Goodman). Any suggestions?

[ATTACH=CONFIG]31930[/ATTACH]
 
Attached Images  
Sponsored Links
  #2  
Old 05-18-14, 04:32 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,470
Received 11 Votes on 8 Posts
Not all systems have a fuse for the transformer. Have you located the transformer and checked to see if it's powered and working (120VAC on input, 24VAC on output)? When you said that there is no voltage at the thermostat, were you checking between terminals R and C?
 
  #3  
Old 05-18-14, 04:58 PM
Member
Thread Starter
Join Date: May 2014
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Yes, I located the transformer and confirmed 120 VAC on input and 24 VAC on output. I did not check between terminals R and C -- I switched out the original thermostat (in guest room) with another functioning one (in hallway) in the house. The original worked at its new location in the hallway, while the functioning one failed to get power when wired into the guest room location. Thank you for your response and any additional suggestions you might have. Your response leads me to believe you're well above my skill level, so I appreciate it,
 
  #4  
Old 05-18-14, 05:06 PM
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,460
Received 0 Votes on 0 Posts
Are they 4 wires T-stat or 5 wires T-stat ??
 
  #5  
Old 05-18-14, 05:07 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,470
Received 11 Votes on 8 Posts
What makes you say that you're not getting power at the thermostat? It appears that you haven't checked to see if there is voltage at the thermostat. What happens when the thermostat calls for cooling? Does the air handler (blower) turn on and blow air? Does the outside unit (compressor & condenser) turn on? There is a condenser fan that is visible from the top of the outside unit. Is that running when the thermostat calls for cooling?
 
  #6  
Old 05-18-14, 05:28 PM
Member
Thread Starter
Join Date: May 2014
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
5-wire t-stat.

I just checked for voltage at the thermostat (between R and C) with negative results. The thermostat is not powering on at all, so the thermostat is not calling for cooling. At the air handler itself, I am able to power on the fan by pressing the contactor.

Thanks again...
 
  #7  
Old 05-18-14, 05:38 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,470
Received 11 Votes on 8 Posts
Do you have a float switch in the condensate pan? Some systems have a safety switch (float) that shuts off the A/C should the condensate not drain and back up, filling the pan. Check to see if you have a float switch and if your pan is full. If that's not the problem, check to see if you have a broken thermostat wire. You should be able to check out the wiring to see if there's an open.
 
  #8  
Old 05-18-14, 07:18 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,689
Received 343 Votes on 321 Posts
I just checked for voltage at the thermostat (between R and C) with negative results.
Now check the same terminals at the control board.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: