New Thermostat not working correctly (Wiring Issue)

I recently purchased a Honeywell Thermostat and tried doing the wiring myself but when I set the thermostat to "cool" the heat turns on.

Blower :
Carrier FA4ANF042

Wires coming from wall:
pink>x
green>G
yellow>Y
white>E
orange>O
red>R

Wiring within thermostat:
W2>E

HELP!
 
Sponsored Links
  #2  
Old 05-20-14, 05:25 PM
Member
Thread Starter
Join Date: May 2014
Posts: 3
Received 0 Votes on 0 Posts


 
  #3  
Old 05-20-14, 05:37 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,372
Received 10 Votes on 8 Posts
wire = old = new
pink>x = tape off
green>G = G
yellow>Y = Y
white>E = Aux/E
orange>O = O/B
red>R = R (leave the factory jumper installed between Rc and R)

You must also configure the new thermostat for heat pump with Aux heat operation or it will heat when you set it to cool.

This is function 1 with the 6000 series thermostat and lower or function 170 with the 7000 series or higher.
 
  #4  
Old 05-20-14, 08:59 PM
Member
Thread Starter
Join Date: May 2014
Posts: 3
Received 0 Votes on 0 Posts
Perfect!

Thank you for your help on this matter!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: