Thermostat Replaced, is it bad?
#1
Member
Thread Starter
Join Date: Jun 2014
Location: USA
Posts: 24
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thermostat Replaced, is it bad?
I replaced a Janitrol 18-60 mercury switched thermostat with a Honeywell TH8320U1008 7day 3/h 2/c Vision PRO 8000. The heat pump is a Goodman combo unit with heat strips.
I wired it up based on the instructions and what I have seen here. I set the thermostat to 2 stage heat with aux heat and the O/B set to energize cool. (pictures of the old and new below). When initially powered, the system was blowing cold air (seemed to be running a little long, but didnt think anything of it). About 2 days after the install, the outdoor unit was running for several hours, but the house temperature started to slowly climb. I did not notice any air moving from the vents. I went and inspected the outdoor unit and there was a little bit of ice on it and suspected an icing condition. I turned power off over night to let it thaw. The next morning, i turned the unit back on and the compressor came on, but still no indoor air movement. I suspected a bad relay for the blower fan, the new thermostat would click when sending the command which told me the relay was working or at least the command was being sent. Since the recent maintenance was the thermostat, I put the old thermostat back on and it worked! Do I have a bad thermostat? Is the outdoor unit looking for a different voltage than what the new thermostat is sending? Thanks for the help
I wired it up based on the instructions and what I have seen here. I set the thermostat to 2 stage heat with aux heat and the O/B set to energize cool. (pictures of the old and new below). When initially powered, the system was blowing cold air (seemed to be running a little long, but didnt think anything of it). About 2 days after the install, the outdoor unit was running for several hours, but the house temperature started to slowly climb. I did not notice any air moving from the vents. I went and inspected the outdoor unit and there was a little bit of ice on it and suspected an icing condition. I turned power off over night to let it thaw. The next morning, i turned the unit back on and the compressor came on, but still no indoor air movement. I suspected a bad relay for the blower fan, the new thermostat would click when sending the command which told me the relay was working or at least the command was being sent. Since the recent maintenance was the thermostat, I put the old thermostat back on and it worked! Do I have a bad thermostat? Is the outdoor unit looking for a different voltage than what the new thermostat is sending? Thanks for the help
#2
Your wiring looked ok. You need to try the FAN ON mode on the new thermostat and see what happens.
#3
Member
Thread Starter
Join Date: Jun 2014
Location: USA
Posts: 24
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I tried system off and fan manual on and the blower did not come on. I also tried system to cool and fan manual on with the same result. For what it is worth, I also tried heat and the blower remained off.
#4
Shorting the red wire to the green wire should bring the fan on. If it doesn't there is an issue at the furnace/air handler.
#5
Member
Thread Starter
Join Date: Jun 2014
Location: USA
Posts: 24
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks PJ. I reinstalled the old Janitrol thermostat and the system is working fine. I just wanted to make sure that I didnt have a wiring or compatibility issue with the new thermostat. I will order a new one and replace it.