A/C not cooling, outside fan not spinning but is w/ stick method, still not cool

Hi guys, really need some help. In true Murphy's Law form, our A/C has decided to quit the weekend before we have a bunch of family coming in from out of town for my son's birthday.

First issue noticed was that the A/C wasn't cooling anymore. Outside temp >90F, inside temp 80+F. I initially thought maybe the filter was clogged (replaced 4 months ago) so I pulled it out to see if that helped -- no luck.

Then I went outside to see the unit, and realized the fan wasn't spinning. I could hear a buzzing sound. I searched through the forum and found the "stick method" which got my fan spinning, but the air is still not cool and the house wasn't cooling down (I let it run for about 15 minutes and the temp went UP a couple degrees -- should I have waited longer?)

We have a Goodman Model CKL49-1L unit. I took a photo of the capacitor since I figured the stick method turning the fan on points to that being an issue -- it isn't bulging or anything. Either way, the air is still not cold from the vents.

Any help/suggestions?
 
Sponsored Links
  #2  
Old 06-17-14, 04:48 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 57,022
Received 835 Votes on 782 Posts
Welcome to the forums.

Change the capacitor as a first step. The second step is to replace the fan motor.
 
  #3  
Old 06-17-14, 06:38 PM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,468
Received 0 Votes on 0 Posts
Is the compressor running ?
 
  #4  
Old 06-17-14, 07:09 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
The compressor probably dropped out on thermal protection when the fan motor stopped.

If the fan spins freely with power removed, I would replace that 40 + 5 x 440 dual cap.

http://securenet.goodmanmfg.com/pdf/...it/RP-466A.pdf
 
  #5  
Old 06-19-14, 01:23 PM
Z
Member
Thread Starter
Join Date: Jun 2014
Posts: 6
Received 0 Votes on 0 Posts
I just picked one up from my local Johnstone Supply. Will install and let you all know.
The fan spins freely with power off, and gets the fan spinning when the power is on.
 
  #6  
Old 06-19-14, 06:53 PM
Z
Member
Thread Starter
Join Date: Jun 2014
Posts: 6
Received 0 Votes on 0 Posts
All good!

Looks like replacing the capacitor did the trick!
Thanks for the help.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: