AC not cooling

Well the title is pretty generic but here is my troubleshooting that I have done.

This system is maybe 15 years old. It is in a house that I am moving into so I don't have much history on how it performed last year.

This year when I first turned on the system, the compressor was not starting. I replaced the capacitor and compressor fires up. It is not making any unusual noises.

The system was not cooling so I first changed the filter and cleaned the A coil. I used the spray non rinsing foam. I also used a cleaner that I got at the local AC supply that I used in a pump sprayer. I flushed the coil with lots of water. Sadly it still has some dirt but leaps and bounds better than before. I also cleaned the condenser coil outside by removing the top and spraying the cleaner and then flushing with water from inside out.

Still not cooling and I noticed that the high pressure line is frosting at the outside unit. It is the same amount of frosting on both sides of the dryer. The 6 capillary tubes at the A coil are also frosting and icing. All of the capillary tubes are frosting/icing equally.

I wanted your thoughts before I have someone come out and take a look. I don't particular trust someone without personal recommendations. I know that this can be a dirty business with people ripping you off and selling you stuff you don't need. Many of these guys are probably paid commissions.

I have not moved into this house yet and I have a couple weeks so i am not in emergency mode. Currently I am painting and replacing flooring before we move in. Would be nice to have colder temps to work in but I can manage for now.
 
Sponsored Links
  #2  
Old 06-18-14, 12:38 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 57,075
Received 836 Votes on 783 Posts
Welcome to the forums.

If you have plenty of airflow now across the A coil then it sounds like your are low on refrigerant.
 
  #3  
Old 06-21-14, 10:22 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 715
Received 0 Votes on 0 Posts
The frosting at the filter drier may indicate a restricted filter/drier.
If the drier is not located within the condenser; I'd pump the system's refrigerant down into the condenser & valve it off.

Remove & replace the filter/drier & see if that helps.
The charge would have to be checked...

Is the indoor airflow strong or weak?
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: