AC won't work with Honeywell RTH8500 WiFi

I have an older Carrier 58gs and I recently bought a Honeywell thermostat RTH8500 wifi unit. The thermostat was relatively easy to hook up and worked fine this winter. I went to turn on the air recently and the outside fan works but the interior blower does not. The thermostat wiring is R to R; W to W; Y to Y and C to C. My furnace is wired R to R; W to W; Y pig tailed to the red wire on the low voltage transducer and C was on either GC or GH or was it Y...darn it (I don't recall). The white wire off the transducer is on the C terminal. Honeywells customer support said to "move the G wire to the C terminal at the thermostat (which was previously done), then move the G wire to the C terminal at the furnace, and then place a jumper wire between the Y terminal and the (now empty) G terminal at the furnace." Because I don't recall if I was on GC or GH, I may be jumping incorrectly. I did a test and a relay sparked more than a relay should. Any advice?
 
Sponsored Links
  #2  
Old 06-22-14, 09:05 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 57,089
Received 840 Votes on 787 Posts
Welcome to the forums.

Gc = fan/cooling
Gh = fan/heating

So you would use a jumper from Gc to Y.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: