A/C compressor fan not starting
My A/C compressor fan does not start when a/c kicks on. The fan motor was making some noise and when I hit the top of the unit blade rotated a revolution, hit it again and it started running, I equate this to passing the stick start test. System cools when running. Not sure but the fan may stop in the middle of cooling but may only stop when a/c goes off and comes back on. A/C company cant make it out for a few days and it seems like its the capacitor and I'm comfortable replacing that. just want conformation on whether the start cap needs to be replaced or the run cap. I believe the run cap is the large cylinder one with "50uf 6uf 440vac" on the side and three terminals, and the start cap is the oval cylinder with 2 terminals. Thanks for any input you guys can give.
#2
You're correct, the Start capacitor is the one that needs to be replaced. However, I can't tell you which one is which. If there is a wiring diagram inside the outside unit, it may show wire colors which may help you determine which is which.
#6
Member
Thread Starter
Join Date: Jun 2014
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Update
So I purchased a 50mF/5mF 440 dual run cap to replace. Was confused when trying to install as the wiring diagram didn't match; no fan wire (purple) and 2 common (red). Upon further investigation the 2nd common (red) was jumping to another 5mF cap with my fan wire (purple) coming off. It seems this is a common way to fix cap issues to only replace the low cap for the fan motor? So I took out both caps and hooked up my new dual run cap connecting all three wires (F,C,H) according to wiring diagram. So far, so good. Just want a heads up if this sounds right to you guys.
#7
Many service guys just carry single capacitors and will just install what's actually needed.
I've always been a big fan of separate capacitors.
What you did sounds fine. If it works ok then you're all set.
I've always been a big fan of separate capacitors.
What you did sounds fine. If it works ok then you're all set.

#8
If I don't have a dual cap in the van but I can do the job with 2 caps and save the customer a trip charge for the parts house I install 2 caps instead of a dual cap. It does seem like separate caps swell up less often but they don't fit as well in many electrical compartments.
If a 45/5 x 440 dual cap reads 0 and 5, I can't install just a 45uF cap. I would worry that the other half will soon fail.
If a 45/5 x 440 dual cap reads 0 and 5, I can't install just a 45uF cap. I would worry that the other half will soon fail.