No Power to outside AC unit
#1
Member
Thread Starter
Join Date: Jul 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
No Power to outside AC unit
I've used my multimeter to test power, none coming to the contactor, so i checked the breaker, reset it, still no power.
checked the line coming to the breaker, no power there. i looked on the inside breaker box, but there is nothing for ac, and no main reset. what am I missing?
checked the line coming to the breaker, no power there. i looked on the inside breaker box, but there is nothing for ac, and no main reset. what am I missing?
#2
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
verify 230v at the inside breaker check each leg to ground 115V..then outside on the concdenser disconnect or at the top of the contactor 230V 115v again...you might be missing a leg and reading across the pair of wires shows nothing.you should have 2 breakers for the AC one condenser 230V the other the air handler/furnace 115v
#3
Your breaker is probably not labeled. I would try turning off all 2 pole breakers and then turning them back on to reset the breaker for the condenser.
There is still the question of why did it trip.
Burned wire? Bad capacitor? High starting amperage? "Grounded" compressor?
There is still the question of why did it trip.
Burned wire? Bad capacitor? High starting amperage? "Grounded" compressor?
#5
Usually the one by the A/C unit is just a shutoff..... not usually an actual breaker.
Now you know where your actual breaker is that controls that A/C compressor.
Houston left you some possible problems.
Now you know where your actual breaker is that controls that A/C compressor.
Houston left you some possible problems.
#6
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
check all of the connections from the contactor thru the shut off into the CB panel...contactor is clean? not black with carbon from arking on start...any bubbling insulation at a connection is an indication of over heating...

#7
Member
Thread Starter
Join Date: Jul 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Trips after a few minutes, the fan ran well, i plan on checking to see if the compressor is grounded. all the connections looked clean/secure during my initial checkup. anything else i should look for.
#8
If the comp was grounded, it would trip immediately I would think. Doesn't mean that its good, partially shorted windings can pull more current. Things heat up and insulation breaks down.
Ideally you put a clamp on amp meter over the different leads and see where the problem is.
Ideally you put a clamp on amp meter over the different leads and see where the problem is.
#9
A clamp on ammeter is ideal otherwise you will have to try running just the fan or just the compressor in which case you are starting to get pretty deep into the wiring.
Let us know if you have a clamp on meter or maybe know someone that has one.
Let us know if you have a clamp on meter or maybe know someone that has one.
#10
A bad run cap can give you a high amperage draw.
Take a look in the panel for a swollen run capacitor or burned wires.
With power removed and while wearing safety glasses, pop the cover off of the compressor terminals to check for melted wires.
Take a look in the panel for a swollen run capacitor or burned wires.
With power removed and while wearing safety glasses, pop the cover off of the compressor terminals to check for melted wires.
#11
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
copper line to any compressor(wires removed) terminal and shows a reading the compressor is grounded then between the terminals show no reading in the 200range or even audble setting the winding is open....smell the freon on a burp from the suction shradder if it burns smelling it the freon is cooked from a burn out...