AC blowing warm air, outside fan not working, capacitor buzzing or humming. Help

Good evening,

My AC is blowing warm air. I checked outside the house and the Fan/Compressor is not working. I tried to move the blades and nothing happens. Opened to check the capacitor and it emits a gentle buzzing sound while the whole system asks for cool air. Once I turn off the system, the sound goes off.

What should I do?

Thank you
 
Sponsored Links
  #2  
Old 07-06-14, 05:33 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,603
Received 338 Votes on 316 Posts
Welcome to the forums.

What buzzes ? Capacitors don't buzz. You have the compressor, the condensor fan or the contactor.

Do you know where the contactor is ?
You'll need to see if the contactor is closing on demand for cold. You need to be careful as it controls 240vac.

Read thru other threads here.... this question is asked every day.
 
  #3  
Old 07-06-14, 05:38 PM
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Hi PJ,

Thanks for your reply.

Probably it is the contactor buzzing. It's near the capacitor. A black piece with 4 cables connected (correct me if I'm wrong). When the whole system is off, there's no sound at all. When the system is on, there's the buzz but the fan won't not start.
 
  #4  
Old 07-06-14, 05:45 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,603
Received 338 Votes on 316 Posts
It sounds like the contactor is working and you need to check the circuit breaker in your panel that runs that unit. You can also check for fuses in the disconnect that is mounted near the unit. Most disconnects are not fused. If you have a meter you can check for 240vac in your disconnect.
 
  #5  
Old 07-06-14, 06:02 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,372
Received 10 Votes on 8 Posts
Was the capacitor swollen on top?

http://www.doityourself.com/forum/at...ing-ac_cap.jpg
 
  #6  
Old 07-06-14, 06:03 PM
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Yes, the breaker was down probably due to a thunderstorm today. I did not check it because the blower was working. Anyway, thanks for your help man!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: