AC blowing warm air, outside fan not working, capacitor buzzing or humming. Help

AC blowing warm air, outside fan not working, capacitor buzzing or humming. Help


  #1  
Old 07-06-14, 05:17 PM
T
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
AC blowing warm air, outside fan not working, capacitor buzzing or humming. Help

Good evening,

My AC is blowing warm air. I checked outside the house and the Fan/Compressor is not working. I tried to move the blades and nothing happens. Opened to check the capacitor and it emits a gentle buzzing sound while the whole system asks for cool air. Once I turn off the system, the sound goes off.

What should I do?

Thank you
 
  #2  
Old 07-06-14, 05:33 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Welcome to the forums.

What buzzes ? Capacitors don't buzz. You have the compressor, the condensor fan or the contactor.

Do you know where the contactor is ?
You'll need to see if the contactor is closing on demand for cold. You need to be careful as it controls 240vac.

Read thru other threads here.... this question is asked every day.
 
  #3  
Old 07-06-14, 05:38 PM
T
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hi PJ,

Thanks for your reply.

Probably it is the contactor buzzing. It's near the capacitor. A black piece with 4 cables connected (correct me if I'm wrong). When the whole system is off, there's no sound at all. When the system is on, there's the buzz but the fan won't not start.
 
  #4  
Old 07-06-14, 05:45 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
It sounds like the contactor is working and you need to check the circuit breaker in your panel that runs that unit. You can also check for fuses in the disconnect that is mounted near the unit. Most disconnects are not fused. If you have a meter you can check for 240vac in your disconnect.
 
  #5  
Old 07-06-14, 06:02 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
  #6  
Old 07-06-14, 06:03 PM
T
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, the breaker was down probably due to a thunderstorm today. I did not check it because the blower was working. Anyway, thanks for your help man!
 
 