Central A/C Outside Unit just humming

Hi: I'm new to this site and of course I have a problem. I have a Trane 14XLI unit that the AC stopped working on yesterday. The outside unit just hums. The fan is NOT locked up and will engage and run if I push start it. But still no cold air. I suspect the compressor is not kicking on. I realize that push starting the fan is esentially bypassing the capacitor. Now my questions: are the fan and the compressor controlled by the same capacitor? I took the side cover off and can only see I capacitor. Is there a way to temporarily bypass the capacitor to see if the compressor will run? Thanks in advance for any responses.
 
  #2  
Old 07-11-14, 08:49 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
No, you don't want to bypass the cap. Yes most units use a dual cap ( 2 caps in one).
 
 