Lennox hp26-024-7p pressure switch lockout
#1
Member
Thread Starter
Join Date: Jul 2014
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Lennox hp26-024-7p pressure switch lockout
I have a Lennox hp26-024-7p that stopped working. I could manually press the contactor to start the compressor and condenser fan, but it would not stay running. We replaced the contactor, now it's showing a pressure switch lockout fault (LED 1 solid, 2 is off).
I tried to jumper the test pin for .5 seconds to reset it, but got nothing. I cut power to the unit, but the light is still on when power is restored. Perhaps I didn't cut power for long enough?
Any thoughts?
I tried to jumper the test pin for .5 seconds to reset it, but got nothing. I cut power to the unit, but the light is still on when power is restored. Perhaps I didn't cut power for long enough?
Any thoughts?
#3
Member
Thread Starter
Join Date: Jul 2014
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I should have mentioned, there is no reset button on the pressure switch, it's automatic. After 3 tries it locks out. I killed power to the unit to try to reset it, but maybe I didn't kill it long enough?
Neither the compressor nor the fan will run while locked out.
Neither the compressor nor the fan will run while locked out.
#4
Did you reset power to the indoor unit, the outdoor unit?
Seems like the .5 second test jumper should have reset it.
I don't see a transformer in the outdoor unit in this manual...
http://www.lennox.com/pdfs/installat...x_HP26_IOM.pdf
Seems like the .5 second test jumper should have reset it.
During a single demand cycle, the defrost control will lock
out the unit after the third time that the circuit is interrupted
by any pressure switch that is wired to the control board. In
addition, the diagnostic LEDs will indicate a locked out
pressure switch after the third occurrence of an open pressure
switch. See table 7. The unit will remain locked out until
power is broken then remade to the control or until the
jumper is applied to the TEST pins for 0.5 seconds.
out the unit after the third time that the circuit is interrupted
by any pressure switch that is wired to the control board. In
addition, the diagnostic LEDs will indicate a locked out
pressure switch after the third occurrence of an open pressure
switch. See table 7. The unit will remain locked out until
power is broken then remade to the control or until the
jumper is applied to the TEST pins for 0.5 seconds.
I don't see a transformer in the outdoor unit in this manual...
http://www.lennox.com/pdfs/installat...x_HP26_IOM.pdf
#7
Member
Thread Starter
Join Date: Jul 2014
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Just got home and cut power to both units for a few minutes. Turned it back on, and after 5 minutes of the anti-short cycle flashing it went back to normal operation.
I appreciate the help. Now the big question, could the bad contactor have caused the pressure switch lockout, or should I dig further into potential problems.
I bought this house as a foreclosure, so I don't really know the maintenance history. I think I'm going to start by having the coils cleaned.
I appreciate the help. Now the big question, could the bad contactor have caused the pressure switch lockout, or should I dig further into potential problems.
I bought this house as a foreclosure, so I don't really know the maintenance history. I think I'm going to start by having the coils cleaned.
#8
A dirty outdoor coil or lack of proper voltage to the outdoor fan motor can trip a high pressure switch.
#9
Member
Thread Starter
Join Date: Jul 2014
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Gotcha. I'll check the voltage. Though the fan has been running steadily and it hasn't tripped again, but it is not cooling the house as fast as I would like, which leads me to suspect a dirty, inefficient coil.
#12
That unit has a dual capacitor that serves the compressor and fan motor.
One or both sides of a dual capacitor can fail causing the motor they serve not to start.
One or both sides of a dual capacitor can fail causing the motor they serve not to start.
#13
Member
Thread Starter
Join Date: Jul 2014
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You called it. I tested the capacitor and that was the problem. Replaced it and it has been running fine since.
I still might have someone come by to see if the unit needs cleaning, but it seems to run fine for now.
Thanks for all your help!
I still might have someone come by to see if the unit needs cleaning, but it seems to run fine for now.
Thanks for all your help!