blower motor
I have a 2ton carrier unit it stopped working the other day. I checked everything and came up with the blower motor is spinning at half speed and the motor is making a knocking noise. I changed the fan relay and still have the problem does this sound like a bad motor or losing power somewhere. And yes it spins freely.
#2
If the motor spins freely and the shaft is tight (meaning it has no lateral movement) then the bearing are probably OK. The windings might be burned out. Or full voltage may not be getting to the motor in which case I think you hear a humming noise and little or no movement. Others can better guide you but I suspect a control circuit is bad.
#5
http://dar.proflo.com/darmanager/Que...USE_TYPE=PARTS
Looks like you have an ICP air handler with an ECM X13 motor.
Did you replace a fan relay in the indoor unit using a soldering iron or the whole control board?
What speed tap terminals are blower motor blue and white using?
Do you have a volt meter?
Looks like you have an ICP air handler with an ECM X13 motor.
Did you replace a fan relay in the indoor unit using a soldering iron or the whole control board?
What speed tap terminals are blower motor blue and white using?
Do you have a volt meter?
#7
What speed tap terminals are blower motor blue and white using at the new control board?
Is blue at 2 and white at 4?
Do you have a volt meter?
Is blue at 2 and white at 4?
Do you have a volt meter?