heat pump help
Old 07-23-14, 09:08 AM
heat pump help
I changed out a Rheem heat pump with a Goodman GSH wired up everything but the new unit seems as though it is reversing the low side line is heating up and the high side is cooling.
I followed the old wiring when hooking up the thermostat.
Tstat - condenser
Blue - common
Orange - orange
White - white
Yellow - yellow
Red- red
The only thing not sure of was the original wiring on the a Rheem white from the tstat went to D on the board if there any suggestions please help.
Old 07-23-14, 10:23 AM
Houston204's Avatar
Received 10 Votes on 8 Posts
The reversing valve on a Rheem / Ruud is the reverse of almost every other brand. You must reconfigure your thermostat O/B terminal to now be O, or move the wire from B to O on the thermostat.
If you post the stat make and model number we can offer further assistance.
Old 07-23-14, 10:37 AM
Houston204's Avatar
B energizes the reversing valve in heat mode and O energizes the reversing valve in cool mode.
Old 07-23-14, 02:43 PM
The thermostat is a Honeywell LR1620
Old 07-23-14, 04:08 PM
Swapped O. Works beautiful thank you