Honeywell TH6220D Thermostat upgrade wiring questions

I am upgrading to a Honeywell TH6220D t-stat.

I currently have an old mercury switch t-stat. Pictures are below.

Name:  IMG_0834.jpg
Views: 6351
Size:  25.5 KBName:  IMG_0835.jpg
Views: 7268
Size:  32.4 KBName:  IMG_0836.jpg
Views: 2047
Size:  32.5 KB

I have a model F+FP060N06B a/c heat pump and electric heater strip in the attic. I think this is considered a 2H/1C unit but am not sure.

The wiring for the old unit shows

Red - R - I believe it is Hot for cool and heat
Green - G - I believe it is Blower
Yellow - Y - I believe it is Compressor
Dk Brown - E - Unknown
Orange - O - Unknown
White - X1 - Unknown
Blue - W2 - Unknown
Extra terminal labeled B with no wires on it.

My new tstat has these connections for a 2H/1C

RC jumpered to R - Power
R jumpered to RC
Y - Compressor contactor
C - 24VAC common
O/B - Changeover Valve
G - Fan Relay
Aux/E - Emergency Heat Relay
L - sends output when on Emer Heat

Trying to figure out which wires on the old go to the new ones.

Thanks in advance for the help.
 
  #2  
Old 08-24-14, 05:59 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 2,101
Received 0 Votes on 0 Posts
New Stat: Red wire to R

Yellow to Y
C not used
Orange to O/B
White to Aux/E
Dark Brown to L
Green to G

Hope this helps.
 
  #3  
Old 08-24-14, 06:54 PM
N
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Thank you very much
Where do you think the Blue wire goes ? It currently is on W2
thanks again.
Norm
 
  #4  
Old 08-24-14, 07:47 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,618
Received 1,604 Votes on 1,478 Posts
What is the model number on the old stat ?

I believe this is the correct wiring. You can confirm the wire colors and connections at the air handler also. Power to the air handler must be shut off when changing wiring.

Red -- R --- > Rc/Rh
Green - G --- > G
Yellow - Y --- > Y
Dk Brown - E --- > Not used.
Orange - O --- > O
White - X1 --- > C
Blue - W2 ---> Aux/E

Blue and dark brown are probably connected together at air handler.
X1 is usually the common wire but white is not its normal color.

Houston, the forum pro, will stop in and confirm.
 
  #5  
Old 08-24-14, 09:08 PM
N
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
The Thermostat is called White-Rodgers. It was put in when they changed over to a heat pump system some years back.
inside the cover reads 2 stage heat / 1 cool
HTG: 1.2 Amps. Max.
CLG: 1.5 Amps. Max.
Max. 30 Volts A>C>
Type 1s8wq-77
LR27935
CLASS 2
156-1854

Thanks
Norm
 
  #6  
Old 08-25-14, 05:46 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
I agree with PJ's wiring.
Remember to remove power to the air handler before replacing the stat.
You must also configure the new stat to control a heat pump with aux heat.
Set function 1 to 5.
 
 