Outside unit wont shut off please help!!!


  #1  
Old 10-09-14, 03:17 PM
S
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Outside unit wont shut off please help!!!

Hello,

My outdoor ac unit will not shut off. on the thermostat when i change it too "system off" only the inside unit turns off, the outside unit stays on. i have checked the contactor on the outdoor unit and it is not stuck. this is a new outdoor unit and a new indoor ac control board. here is what i have done

Replaced Thermostat
checked contactor
removed contactor and cleaned contacts
replaced indoor control board
moved thermostat wires and tried different combinations

it will blow cold when i keep the system on cool and the fan on. currently that is what we are doing to keep the house cool, we are just unplugging it ever 3-4 hours and letting it rest.

please help!!
 
  #2  
Old 10-09-14, 03:35 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,554
Received 59 Upvotes on 50 Posts
If you disconnect one or both of the control wires (24VAC) where they come into the outside unit, does the outside unit turn off? This will tell you whether the problem lies inside the house or in the outside unit. If you disconnect the control signal wires where they come into the outside unit and it turns off, the problem is somewhere inside the house (something is always sending 24VAC to the outside unit). Conversely, if the outside unit continues to run with the control wires disconnected, the problem lies in the outside unit.
 
  #3  
Old 10-09-14, 03:43 PM
S
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok i did that and when the wires are disconnected the outdoor unit turns off, so the problem is inside.. what could it be?
 
  #4  
Old 10-09-14, 03:56 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,554
Received 59 Upvotes on 50 Posts
Are you sure that you wired the new control board correctly? Was it an exact replacement, or was it slightly different from the original board? Do you have a circuit diagram of the indoor system?
 
  #5  
Old 10-09-14, 04:35 PM
S
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
It was not the exact model number but the board worked for about a week
 
  #6  
Old 10-09-14, 05:11 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
Welcome to the forums!! To better assist, can you post the model number of your inside and outside units?

moved thermostat wires and tried different combinations
How is the thermostat currently wired at the thermostat and at the control board? Which wires are going to the outside unit?

You should have two wires going to the outside unit contactor and they should be connected to C and Y at the control board. Once we get the model numbers we can figure out the correct wiring.
 
  #7  
Old 10-09-14, 08:53 PM
S
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hey,
Currently the outdoor two wires are connected to R and B, b is common in my unit
 
  #8  
Old 10-09-14, 09:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
R is 24vac and B is common. If you use those terminals the condensor will never shut off.

You should be using common and Y for the condensor.
 
  #9  
Old 10-10-14, 07:13 AM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
Currently the outdoor two wires are connected to R and B, b is common in my unit
There's your problem. As PJMax stated, with a constant 24V going to the condenser it will never turn off. That is a constant 24V feed directly from the transformer.

Remove R wire from condenser. As stated previously, you need to have a wire from Y terminal and a wire from common terminal (B) going to the condenser. Make sure you have two wires on (Y) at the control board; one from Y at the thermostat and the one going to the condenser.

Having B as a common, you probably have a Trane or American Standard unit. Do you have a wire connected to the thermostat coming from B at the control board? If so, the B wire from the control board should be connected to C at the thermostat.
 
  #10  
Old 10-10-14, 11:44 AM
S
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok I connect the outdoor to y and b, now it won't come on at all, only the indoor fan will
 
  #11  
Old 10-10-14, 11:51 AM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
It sounds like you have an issue with the other wires connected to the thermostat and/or control board or you blew the fuse on the control board. If you did not turn off power to the unit before switching wires it is probably the fuse on the control board. Turn off power to the unit and look for an automotive type fuse (probably purple or amber colored) to see if it blew. If so, you will have to replace that fuse to restore operation.
 
Attached Images  
  #12  
Old 10-10-14, 04:56 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
I doubt it's a fuse or the blower wouldn't work.

Can you take a picture of your control board and post it here for us ?
http://www.doityourself.com/forum/el...rt-images.html

Your problem is that you changed several parts and probably didn't get all the wires back in their correct places.
 
  #13  
Old 10-10-14, 05:19 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
I doubt it's a fuse or the blower wouldn't work.
Who knows? Since he installed a new control board, he might have one of the blower motor leads connected to PRI-1. I surely hope not. But you are correct; more than likely not a fuse issue.
 
  #14  
Old 10-26-14, 11:43 AM
W
Member
Join Date: Jan 2014
Location: USA
Posts: 630
Upvotes: 0
Received 0 Upvotes on 0 Posts
Were it me , I would disconnect the tstat wires and the 2 wires going to the condenser , ( the indoor unit ) .

With a volt meter , I would measure voltage from R to B ( common ) . 24 VAC ?

If so , I would jumper from R to G . Does the fan come on ?

If so , move the jumper to R to W . Does heat come on ?

Re-install the 2 wires going to the condenser , Y and B ( common ) .

Now , move the jumper from R to Y . Does the condenser unit come on ?

Let us know your results .

God bless