outside AC system not running


  #1  
Old 03-24-15, 07:08 PM
C
Member
Thread Starter
Join Date: Mar 2015
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
outside AC system not running

We had some construction done and the workers put plywood over the top of the outside AC system to do work. I forgot about it and let the AC run. So of course, it no longer works, but the failure is not what I expected.

When I use the thermostat to cause the AC to turn on, the inside blower works, but the air is not cold. When I look at the outside unit, it is not on.

I opened up the unit and pressed down on the contact, and the fan and compressor started right up, so obviously they're both working, the capacitor is working, and power is getting to the unit. I expected a fuse to be blown or the compressor to have gone bad.

So is it simply the contact or the thermostat? I'm not sure what else could have gone wrong, but I don't see how covering the unit could have caused either of those to have problems. How would you debug the issue without just replacing them both and hoping?
 
  #2  
Old 03-24-15, 07:46 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,480
Received 90 Upvotes on 83 Posts
Many outdoor units have a pressure switch that has a manual reset button.



What brand is this unit?

Some older Rheem units had the reset on the outside.



The reset button is usually inside of the outdoor unit.

This old Lennox has a manual reset pressure switch on the left side.



Disregard the mice. It was an old jab at anther tech.
 
  #3  
Old 03-24-15, 08:02 PM
C
Member
Thread Starter
Join Date: Mar 2015
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
It's a Ruud system. How did I not know about that little switch?!? I went out and found it, pressed it, and heard a click. That gave me hope! So I went back in, hit the thermostat, and voilà, cold air!

Thank you!
 
 