condensate overflow switch not installed

I had a brand new Trane 3T heat pump installed by an AC tech. AC tech didn't install overflow switch and there is no secondary drain. The old one didn't have it and I forgot to request. The Air handler is on the first floor.

Placed a water alarm near the air handler.

If the primary drain is clogged, how much damage will it have for the air handler itself? Isn't portion of the coil submerged in water?

Eventually I will install one. But I wonder if I should do it sooner or later?
My main concern is if the brand new AC will be damaged because of condensate.

Another question is: it seems it's pretty easy to install. Just cut open the red wire to AC and hook it up to the switch. Open the spot for secondary drain and put in the unit. is this correct?
 
  #2  
Old 05-19-15, 02:40 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
if the AHU is in occupied area I would do it ASAP. Yes that's how you should install it.
 
  #3  
Old 05-20-15, 05:54 AM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,491
Upvotes: 0
Received 8 Upvotes on 8 Posts
auxiliary drain pans and wet switches are 100% necessary when a unit is located in an area that could be damaged by water. This is pretty much everywhere but a basement.
 
  #4  
Old 05-20-15, 01:10 PM
R
Member
Thread Starter
Join Date: Aug 2010
Location: usa
Posts: 235
Received 0 Upvotes on 0 Posts
Thank both for replies.
What are good brands to use and where to buy (in addition to amazon) without requiring license?
 
  #5  
Old 05-20-15, 02:16 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Try hvacpartsoutlet.com. It's about $38.
 
 