A/C unit disconnect wiring?
#1
Member
Thread Starter
Join Date: May 2015
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
A/C unit disconnect wiring?
Bought used mobile home. Tear down process while disconnecting A/C unit I observed wiring. 10/3 wire with grounds cut off for feed and THHN to unit. 2 black, 2 red, I know both hot,no need for neutral. There is a green THHN connected to middle bus and and the white wire of the 10/3 feed connected to middle bus. The white is also connected to the isolated neutral bus in the main panel. From what I know and researched this is wrong!! Why was it done this way and why us it working and shoukd i redo it?
#2
Member
Join Date: Jan 2014
Location: USA
Posts: 630
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You have only one panel supplying the home & the A/C ?
If so , that makes it a service entrance panel . You probably have a green screw going through the neutral bar & threaded into the metal " can " ( enclosure ) of the panel . This , for all practical purposes , means that grounds and neutrals were terminated on the neutral bar . ( I like to add a separate ground bar . )
If there is a main before power gets to the panel , than the neutrals are on the neutral bar and grounds on the ground bar & no green screw through the neutral bar .
Let us know and I will reccomend corrective action .
God bless
Wyr
If so , that makes it a service entrance panel . You probably have a green screw going through the neutral bar & threaded into the metal " can " ( enclosure ) of the panel . This , for all practical purposes , means that grounds and neutrals were terminated on the neutral bar . ( I like to add a separate ground bar . )
If there is a main before power gets to the panel , than the neutrals are on the neutral bar and grounds on the ground bar & no green screw through the neutral bar .
Let us know and I will reccomend corrective action .
God bless
Wyr
#4
Member
Join Date: Jan 2014
Location: USA
Posts: 630
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Then you should have 2 hots , a neutral and an earth ground coming into the house panel . You should have a ground bar screwed to the panel can / enclosure and the neutral bar should not be bonded to the panel can / enclosure .
All the earth grounds should be moved to the newly installed ground bar . Any white conductors being used as an equipment grounding conductor can be marked with green tape , at each end , to identify them as grounds ( and not neutrals ) .
God bless
Wyr
All the earth grounds should be moved to the newly installed ground bar . Any white conductors being used as an equipment grounding conductor can be marked with green tape , at each end , to identify them as grounds ( and not neutrals ) .
God bless
Wyr
#6
Why would technician have cut grounds and used white as ground then connected to neutral in panel?