Blower not working for air but does for heat


  #1  
Old 05-31-15, 02:37 PM
W
Member
Thread Starter
Join Date: May 2015
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Blower not working for air but does for heat

I have a Central Electricbrand furnace for modular Home model eb20b. The fan blower stopped working. It comes on with heat but not air. I replaced the thermostat and still nothing. The fuses are all on so what's my next step? I just paid to have the outside fan motor ,,blade and capacitor replaced 10 days ago.
 
  #2  
Old 05-31-15, 03:23 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Most likely the blower relay needs to be replaced. Google relay 3110-3301.
 
  #3  
Old 05-31-15, 03:57 PM
W
Member
Thread Starter
Join Date: May 2015
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is it hard to replace? That last service gutted me. Thank you I'm advance
 
  #4  
Old 05-31-15, 04:07 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,418
Received 74 Upvotes on 67 Posts
It is easy to replace the relay.
It would be safer if you turn off the breakers to the air handler as well as the 2 breakers in the air handler.

Name:  EVcon EB15b.jpg
Views: 2011
Size:  27.9 KB

Name:  Evcon EB20B diagram.jpg
Views: 8465
Size:  53.0 KB
 
  #5  
Old 05-31-15, 04:42 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,418
Received 74 Upvotes on 67 Posts
http://www.amazon.com/Replacement-No.../dp/B00IBN0W3I

It looks like that relay is $20.

2 screws and 6 wires.
 
  #6  
Old 05-31-15, 04:53 PM
W
Member
Thread Starter
Join Date: May 2015
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the help. I really appreciate it
 
  #7  
Old 05-31-15, 06:03 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,418
Received 74 Upvotes on 67 Posts
You are very welcome.

High voltage is present in that unit. Remember to turn off the breakers before replacing the relay.

I usually snap a picture or 2 before replacing parts.
 
  #8  
Old 05-31-15, 06:23 PM
W
Member
Thread Starter
Join Date: May 2015
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Will do. Glad it's a cool May here in Hot Springs Arkansas. Thanks again
 
  #9  
Old 05-31-15, 06:28 PM
W
Member
Thread Starter
Join Date: May 2015
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Looking at these diagrams is confusing to me. Where do I start to look? Do I have to remove the fan and motor
 
  #10  
Old 05-31-15, 07:05 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,418
Received 74 Upvotes on 67 Posts
The black and white diagram is your component arrangement.

If this air handler is vertically installed in an upflow application, I would expect to remove the top panel and see the fan relay on the top left portion of the control area.

if it is a down flow application the controls would be in the lower portion of the air handler.

Name:  Evcon EB panel.jpg
Views: 793
Size:  25.7 KB
 
  #11  
Old 05-31-15, 07:21 PM
W
Member
Thread Starter
Join Date: May 2015
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Carlos I owe you a cold one my friend. Thank you again for your energy and time. You saved my vacation money and my girlfriends much happier now. Its at the bottom and I will find it.
 
  #12  
Old 06-01-15, 10:19 AM
W
Member
Thread Starter
Join Date: May 2015
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Got the part local for 10.71 and it works great. Thank you again.
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: