Blower not working for air but does for heat

I have a Central Electricbrand furnace for modular Home model eb20b. The fan blower stopped working. It comes on with heat but not air. I replaced the thermostat and still nothing. The fuses are all on so what's my next step? I just paid to have the outside fan motor ,,blade and capacitor replaced 10 days ago.
 
Sponsored Links
  #2  
Old 05-31-15, 03:23 PM
Member
Join Date: Feb 2014
Location: USA
Posts: 2,103
Most likely the blower relay needs to be replaced. Google relay 3110-3301.
 
  #3  
Old 05-31-15, 03:57 PM
Member
Thread Starter
Join Date: May 2015
Posts: 7
Is it hard to replace? That last service gutted me. Thank you I'm advance
 
  #4  
Old 05-31-15, 04:07 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,325
Likes Received: 1
It is easy to replace the relay.
It would be safer if you turn off the breakers to the air handler as well as the 2 breakers in the air handler.

Name:  EVcon EB15b.jpg
Views: 1118
Size:  27.9 KB

Name:  Evcon EB20B diagram.jpg
Views: 3789
Size:  53.0 KB
 
  #5  
Old 05-31-15, 04:42 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,325
Likes Received: 1
http://www.amazon.com/Replacement-No.../dp/B00IBN0W3I

It looks like that relay is $20.

2 screws and 6 wires.
 
  #6  
Old 05-31-15, 04:53 PM
Member
Thread Starter
Join Date: May 2015
Posts: 7
Thanks for the help. I really appreciate it
 
  #7  
Old 05-31-15, 06:03 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,325
Likes Received: 1
You are very welcome.

High voltage is present in that unit. Remember to turn off the breakers before replacing the relay.

I usually snap a picture or 2 before replacing parts.
 
  #8  
Old 05-31-15, 06:23 PM
Member
Thread Starter
Join Date: May 2015
Posts: 7
Will do. Glad it's a cool May here in Hot Springs Arkansas. Thanks again
 
  #9  
Old 05-31-15, 06:28 PM
Member
Thread Starter
Join Date: May 2015
Posts: 7
Looking at these diagrams is confusing to me. Where do I start to look? Do I have to remove the fan and motor
 
  #10  
Old 05-31-15, 07:05 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,325
Likes Received: 1
The black and white diagram is your component arrangement.

If this air handler is vertically installed in an upflow application, I would expect to remove the top panel and see the fan relay on the top left portion of the control area.

if it is a down flow application the controls would be in the lower portion of the air handler.

Name:  Evcon EB panel.jpg
Views: 383
Size:  25.7 KB
 
  #11  
Old 05-31-15, 07:21 PM
Member
Thread Starter
Join Date: May 2015
Posts: 7
Carlos I owe you a cold one my friend. Thank you again for your energy and time. You saved my vacation money and my girlfriends much happier now. Its at the bottom and I will find it.
 
  #12  
Old 06-01-15, 10:19 AM
Member
Thread Starter
Join Date: May 2015
Posts: 7
Got the part local for 10.71 and it works great. Thank you again.
 