A/C Unit Not Coming On

My problem is similar. No 24 volt power to the condensing unit outside. The thermostat has 24 volt (C+R) but not C+Y. Checked Furnace in attic and found 24 volt power again C+R but not C+anything else. The control board led status light stays on solid red.My furnace is an 8 year old Payne but it's only been used the last year.
What do you think?
 
Sponsored Links
  #2  
Old 06-04-15, 03:09 PM
Member
Join Date: Feb 2014
Location: USA
Posts: 2,104
Received 0 Votes on 0 Posts
With stat off you won't have power on Y. Try jumping R to Y. The ouside unit should run. Let's us know.
 
  #3  
Old 06-04-15, 03:34 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,689
Received 343 Votes on 321 Posts
Welcome to the forums.

I moved you to your own thread so as to not get the systems mixed up.

Don't forget many thermostats have a five minute delay in energizing the Y terminal for compressor protection.
 