Looking for advice on troubleshooting an air handler. Problem description is as follows:

Thermostat fan setting to on, but no air coming through ducts. Checked circuit breakers and voltage behind thermostat (RC - W) and received 26 VAC. Outside heatpump fan turns on normally.

Things I'm about to check: Air handler is in the attic, will check the relay to hear if it energizes when thermostat fan switch is set to ON, and inspect for ice, water in safety switch (not sure if this is equipped or not), and control board fuse if blown. Question I have though: If the voltage is correct at the thermostat, would this also mean the control board is operating normally?

Thank you in advance for any replies.
 
Sponsored Links
  #2  
Old 06-07-15, 10:28 AM
Member
Join Date: Feb 2014
Location: USA
Posts: 2,104
Received 0 Votes on 0 Posts
Are you trying to run it in heat mode?
 
  #3  
Old 06-07-15, 10:31 AM
Member
Thread Starter
Join Date: Jun 2015
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
No, only in cold mode, forgot to mention that.
 
  #4  
Old 06-07-15, 10:55 AM
Member
Join Date: Feb 2014
Location: USA
Posts: 2,104
Received 0 Votes on 0 Posts
Take off R and G wires at stat and twist them together. See if the blower starts.
 
  #5  
Old 06-07-15, 11:09 AM
Member
Thread Starter
Join Date: Jun 2015
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
I just got back down from the attic and confirmed that the blower motor isn't turning when the system is on, additionally there's water leaking out of a pipe fitting with water dripping down to the section where the motor assembly is located. I'll try jumping R and G and see if that does anything.
 
  #6  
Old 06-07-15, 11:48 AM
Member
Thread Starter
Join Date: Jun 2015
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
I got it going.... I had the system off for about 30 minutes in case there was any ice formed anywhere on the condenser and wiped all traces of water drips. I reset the fuse on the control board, and then turned the system back on, and now I have air going through the vents. I'm not sure what I fixed, but I'm not complaining, I'll inspect the unit for leaks throughout the day.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: