Carrier Infinity model 24ANA 3-Ton Split System
#1
Member
Thread Starter
Join Date: Jun 2015
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts

I have a error code 82-Thermal Lockout in high state 4 hours. I read where I might have to reset the lockout temp a few degrees in maintenance mode. I am just not sure how to do this. We are having exceptionally high outside temperatures. I was told also to just let the compressor cool down. Any help with this would be appreciated. Thanks Ralph
#2
It appears from the installation manual that to reset the error condition, you can either wait 4 hours, or recycle the 24V power (turn off the power to the A/C system and then turn it back on).