Refrigerant flow

If the refrigerant metering device is restricted , will this result in the suction pressure and temperature being abnormally low ? The high side pressure abnormally high ? Assuming the system is properly charged ?

I am not asking for specific pressures , just a generalization .

Thanks ,
Wyr
God bless
 
Sponsored Links
  #2  
Old 06-27-15, 08:03 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,372
Received 10 Votes on 8 Posts
Sometimes.

It could also be one of those 2 symptoms with a txv.

It is easier to see when a BB sized piece of solder is against the piston at the evaporator coil. It will pump down. Swedges are involved almost every time that I see this. A 3/8" coupling is not very expensive.
 
  #3  
Old 06-27-15, 11:01 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 715
Received 0 Votes on 0 Posts
The high-side will not usually be excessively high but the subcooling will be high.

I swaged tubing for many decades, all the time, & never had a problem with restrictions...evidently they weren't doing it right.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: