24 Volt not reaching T-Stats

Problem was my condensing unit fan was not spinning.

- Tested 24 volt going through contact came out nothing
- Tested 24 volt going through my T-stats and came out nothing
- Tested 24 volt going through my Transformer Out and I do see the 24 volts
- Flashing red and green light

What would be my next step?
 
  #2  
Old 07-19-15, 12:11 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,554
Received 59 Upvotes on 50 Posts
Are the flashing Red/Green lights on your furnace control board? If so, what does your furnace manual say it means? Also, have you checked to see if there is a fuse on your furnace control board? Many newer furnaces fuse the 24VAC line so that a short circuit on the 24V line doesn't damage the transformer.
 
  #3  
Old 07-19-15, 12:36 PM
Y
Member
Thread Starter
Join Date: Jul 2015
Location: Canada
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
The Flashing red and green light mean its normal, as for the fuse I'm not sure which one it is. If i have to assume its the purple tab with the 3 on my picture. I have not check the fuse to see if its burnt or anything. I tested the blue and yellow wire coming out from the transformer and that's where i see the 24 volts if that's how you correctly test it.



 
  #4  
Old 07-19-15, 12:40 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,554
Received 59 Upvotes on 50 Posts
I don't see a picture, however 3A is a common fuse amperage for the 24V fuse. If the fuse is blown, you'll need to find out why, as fuses rarely blow for no reason.
 
  #5  
Old 07-19-15, 12:48 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,427
Received 75 Upvotes on 68 Posts
The outdoor fan motor is not spinning.

Does the compressor outside run with a cooling demand?
Does the indoor fan turn off and on from the thermostat?

You tested the transformer correctly but did you measure R to C at the furnace terminals with the door switch depressed?

Sounds like you have a Lennox furnace.
 
  #6  
Old 07-19-15, 12:50 PM
Y
Member
Thread Starter
Join Date: Jul 2015
Location: Canada
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
The fuse tested fine. tell me if you can see the image now.

Name:  20150719_153022 22222.jpg
Views: 204
Size:  30.2 KB
 
  #7  
Old 07-19-15, 12:53 PM
Y
Member
Thread Starter
Join Date: Jul 2015
Location: Canada
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
The fuse tested fine. tell me if you can see the image now.Name:  20150719_15295522222.jpg
Views: 197
Size:  40.3 KB
 
  #8  
Old 07-19-15, 12:57 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,427
Received 75 Upvotes on 68 Posts
Your pictures are coming thru now.

I haven't been able to find a Lennox diagnostic code chart that lists open fuse?
That is strange.

I take it that you have power between R and C at the furnace?
 
  #9  
Old 07-19-15, 01:03 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,554
Received 59 Upvotes on 50 Posts
I'm seeing the images now also. As Houston said, did you measure the 24VAC between the R & C terminals on the terminal strip near the bottom of the board (as shown in your picture)? As Houston also mentioned, you need to tape the door switch closed so that the furnace is powered up.
 
  #10  
Old 07-19-15, 05:18 PM
Y
Member
Thread Starter
Join Date: Jul 2015
Location: Canada
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
OK, so I made a mistake on the test earlier while I was outside at the condenser.
So the brown wire coming up is from the inside Furnace, if I put my leads on the two orange tab inside I would get my 24 volts.
[ATTACH=CONFIG]53570[/ATTACH]

Now if you looked at my previous picture the black wire that goes into the tab stays black coming out, as for the white wire it becomes yellow. Now that yellow wire goes down to this green thing and out and into the contacter.
[ATTACH=CONFIG]53572[/ATTACH]
[ATTACH=CONFIG]53573[/ATTACH]


If I put my leads on the blue and black wire while its pulled off. I would read 10 volts. But if I would put my leads on the two contact while its both clip on, I would read zero.

[ATTACH=CONFIG]53571[/ATTACH]


So my question is my contactor the problem or that green thing? Because if I push my contactor down, everything will work. But since the 24 volts isn't going through to pull the magnet down it won't work.
 
Attached Images     
  #11  
Old 07-19-15, 05:28 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
The green thing is the high pressure safety switch. Try pressing the reset button.
 
  #12  
Old 07-19-15, 05:44 PM
Y
Member
Thread Starter
Join Date: Jul 2015
Location: Canada
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
Its too late for me to test it now, ill have to test it tomorrow. When you say the reset switch I'm going to assume the red button on top of it? Do I just hit it once or hold it or something?
 
  #13  
Old 07-19-15, 05:48 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Just press in and you should hear click. Yes red button.
 
  #14  
Old 07-19-15, 07:49 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
Did you check for 24vac here first ? See if it changes when the contactor wires are removed.

Name:  check1.jpg
Views: 183
Size:  16.8 KB
 
  #15  
Old 07-19-15, 07:56 PM
Y
Member
Thread Starter
Join Date: Jul 2015
Location: Canada
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes I did get 24 volts there.
 
  #16  
Old 07-20-15, 04:49 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,427
Received 75 Upvotes on 68 Posts
Does the run capacitor appear swollen on the terminal side?

A weak cap can trip that pressure switch.
 
  #17  
Old 07-21-15, 06:23 PM
Y
Member
Thread Starter
Join Date: Jul 2015
Location: Canada
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hitting the High Pressure Safety Switch worked. It fixed the problem. Thank you.
 
  #18  
Old 07-21-15, 10:09 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
Hitting the High Pressure Safety Switch worked. It fixed the problem
It will probably trip again.

Houston mentioned an issue above and if not that..... you could be having a problem with the condenser fan.
 
  #19  
Old 07-22-15, 11:37 AM
Y
Member
Thread Starter
Join Date: Jul 2015
Location: Canada
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
The cap is perfectly fine. Doesnt look swollen and it tested fine. The cap was the first thing i tested.
 
 