New unit high humidity ?

April 10, 2015 had new heil installed 14 seer only difference from old unit 2.5 ton is they installed a 3 ton N coil Inside . Temp split is 18. Humidity level runs from 66 to 73 % ? Any help is greatly appreciated.
 
  #2  
Old 07-20-15, 08:48 AM
B
Member
Join Date: Oct 2008
Location: New England
Posts: 9,457
Received 47 Upvotes on 43 Posts
When they oversize an ac system it cools in short bursts and doesn't run long enough to remove the moisture. Not a pro on ac units, they will be along, but some will have a dehumidify mode.

Does yours run continuously or in short cycles?

Bud

By the way, welcome to the forum.
 

Last edited by Bud9051; 07-20-15 at 08:49 AM. Reason: addition
  #3  
Old 07-20-15, 10:07 AM
H
Member
Thread Starter
Join Date: Jul 2015
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Short cycles I have fan on was told that is better for uv light
 
  #4  
Old 07-20-15, 10:10 AM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 18,873
Received 1,189 Upvotes on 1,146 Posts
What? You have a UV filter in the return so the fan is running to keep air moving across it?

Short cycles mean the AC doesn't run long enough to remove humidity. As Bud said, classic symptom of an oversized system.
 
  #5  
Old 07-20-15, 10:16 AM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,553
Received 59 Upvotes on 50 Posts
In addition to the oversized unit contributing to high humidity, leaving the fan (blower) running continuously will also. You have some water in your condensate pan. When the fan runs with compressor off, you're adding humidity by blowing air over a pan of water, similar to the way a humidifier works. I don't know how much humidity it will add, but I've read that it will add some.
 
  #6  
Old 07-20-15, 10:52 AM
H
Member
Thread Starter
Join Date: Jul 2015
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes a uv filter in return was told to leave fan on to keep circulating air through filter. Setting to auto and will discuss the coil with the installer, he swears it's not oversized that the coil being bigger makes it more efficient. 😁 thx for all the help
 
  #7  
Old 07-20-15, 10:57 AM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,491
Upvotes: 0
Received 8 Upvotes on 8 Posts
seer makes the unit more efficient. Turn your blower to auto. This will lower your RH hopefully 8-12%
 
  #8  
Old 07-20-15, 11:12 AM
H
Member
Thread Starter
Join Date: Jul 2015
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you done, how long roughly till rh starts to drop ?
 
  #9  
Old 07-20-15, 12:35 PM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,491
Upvotes: 0
Received 8 Upvotes on 8 Posts
a day or two. your unit should not cycle at all today.
 
  #10  
Old 07-20-15, 02:30 PM
H
Member
Thread Starter
Join Date: Jul 2015
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks everyone so far dropping
 
 