Blower fan won't shut off

About a year ago while running my a/c the fan on my older amana furnace, It has a white rodgers 50a51-215 board started to run full time.
it showed a code (heat called for none detected) was told i needed a new board

new board worked fine till last week same story only no code.At that time i noticed water in the area of the board from a plugged drain and assumed
the water was killing the board.
today put a new board on same story.is their something else that can kill these things or should i just give the go ahead on a six thousand dollar bid that i got
last week.yea stuff is expensive in California.


Any help would be greatly appreciated

allan
 
  #2  
Old 07-26-15, 09:06 AM
Former Member's Avatar
Member
Join Date: May 2006
Location: US
Posts: 726
Upvotes: 0
Received 0 Upvotes on 0 Posts
Amana hmmmm here is what I would probably do first. If a split system you need to disconnect the white tstat wire from the outside unit to the air handler. Do that and get back on here (if that works) and I will tell you what your problem is and exactly what to do about it.
 
  #3  
Old 07-26-15, 09:32 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Which fan are you talking about, in the air handler or condenser?
Geo
 
  #4  
Old 07-27-15, 05:58 AM
A
Member
Thread Starter
Join Date: Jul 2015
Location: usa
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
The fan that is running constantly is the air handler
 
  #5  
Old 07-27-15, 06:04 AM
A
Member
Thread Starter
Join Date: Jul 2015
Location: usa
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
I will try disconnecting the low voltage from the condenser today.
I did try that from the thermostat side with no success
 
  #6  
Old 07-27-15, 11:54 AM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,402
Upvotes: 0
Received 5 Upvotes on 5 Posts
FORMER... I don't understand why you want to disconnect that T-stat wire from outside. Do you just want to shut down the condenser ??
 
  #7  
Old 07-27-15, 06:00 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
I changed the title to better represent your problem.

These control boards are fairly reliable but they don't like water.

I would doubt your problem has anything to do with outside wiring.
You just put in a brand new board and the LED is doing nothing ?

With many control boards... an open or intermittent safety stat in the furnace can cause the fan to run.

Things you can try....
Be sure there is +/- 24vac on the R and C terminals.
Try disconnecting the G terminal wire.
Actually.... disconnect the R terminal wire as that will take the thermostat out of the equation.
 
  #8  
Old 07-30-15, 05:40 PM
A
Member
Thread Starter
Join Date: Jul 2015
Location: usa
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Well we have air again Thank you to all who replied.
Turns out the new board is good. My neighbor put in a jumper
so we could turn on the blower manually and allow the thermostat
to cycle the system.when i replaced the board i neglected to take
out the jumper.wired the board correctly and back in business

I believe it was the plugged drain tube that ruined the original board
again Thank you and good day