Blower fan won't shut off
About a year ago while running my a/c the fan on my older amana furnace, It has a white rodgers 50a51-215 board started to run full time.
it showed a code (heat called for none detected) was told i needed a new board
new board worked fine till last week same story only no code.At that time i noticed water in the area of the board from a plugged drain and assumed
the water was killing the board.
today put a new board on same story.is their something else that can kill these things or should i just give the go ahead on a six thousand dollar bid that i got
last week.yea stuff is expensive in California.
Any help would be greatly appreciated
allan
it showed a code (heat called for none detected) was told i needed a new board
new board worked fine till last week same story only no code.At that time i noticed water in the area of the board from a plugged drain and assumed
the water was killing the board.
today put a new board on same story.is their something else that can kill these things or should i just give the go ahead on a six thousand dollar bid that i got
last week.yea stuff is expensive in California.
Any help would be greatly appreciated
allan
#2
Amana hmmmm here is what I would probably do first. If a split system you need to disconnect the white tstat wire from the outside unit to the air handler. Do that and get back on here (if that works) and I will tell you what your problem is and exactly what to do about it.
#7
I changed the title to better represent your problem.
These control boards are fairly reliable but they don't like water.
I would doubt your problem has anything to do with outside wiring.
You just put in a brand new board and the LED is doing nothing ?
With many control boards... an open or intermittent safety stat in the furnace can cause the fan to run.
Things you can try....
Be sure there is +/- 24vac on the R and C terminals.
Try disconnecting the G terminal wire.
Actually.... disconnect the R terminal wire as that will take the thermostat out of the equation.
These control boards are fairly reliable but they don't like water.
I would doubt your problem has anything to do with outside wiring.
You just put in a brand new board and the LED is doing nothing ?
With many control boards... an open or intermittent safety stat in the furnace can cause the fan to run.
Things you can try....
Be sure there is +/- 24vac on the R and C terminals.
Try disconnecting the G terminal wire.
Actually.... disconnect the R terminal wire as that will take the thermostat out of the equation.
#8
Member
Thread Starter
Join Date: Jul 2015
Location: usa
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Well we have air again Thank you to all who replied.
Turns out the new board is good. My neighbor put in a jumper
so we could turn on the blower manually and allow the thermostat
to cycle the system.when i replaced the board i neglected to take
out the jumper.wired the board correctly and back in business
I believe it was the plugged drain tube that ruined the original board
again Thank you and good day
allan
Turns out the new board is good. My neighbor put in a jumper
so we could turn on the blower manually and allow the thermostat
to cycle the system.when i replaced the board i neglected to take
out the jumper.wired the board correctly and back in business
I believe it was the plugged drain tube that ruined the original board
again Thank you and good day