Inside blower shuts off during cooling
So I have a strange issue with my hvac. The inside blower fan works in the on and circ mode when not on cool or heat. When I put it on cool the fan works in the on, auto and circ mode but it shuts off after a few minutes and the compressor/condenser keeps running outside. After a few minutes the blower kicks backs on. I just went down with my multimeter to see what was going on but the blower has been continuously running for the last thirty minutes. I don't know where to go from here. It's a goodman air handler and compressor/condenser. The control board inside the air handler was replaced about 7 months ago (pcbbf112). Any help is appreciated.
#2
Since it appears to be somewhat intermittent (working OK currently), the first thing I would do is to check for loose or broken wires around the thermostat and control board.
#3
Member
Thread Starter
Join Date: Jul 2015
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Checked for loose wires doesn't seem to be an issue. It's strange that the fan runs no problem when not on cool/heat. Ta managed to drop the house temp 3 degrees in the last few hours. I do notice that the fan does seem to be running on a low speed right now I think? I don't know if it's a multi speed blower or not.