Is it normal to see some minor pitting or sooting/blackening of the pad contact points of an AC contactor?
 
Sponsored Links
  #2  
Old 08-14-15, 02:42 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,496
Received 15 Votes on 10 Posts
Yes, since the contactor is switching inductive loads (compressor and condenser fan motors), it's normal to get a little arcing when the contacts open & close. As long as the contacts aren't badly pitted to where there's little contact left, you should be okay.
 
  #3  
Old 08-14-15, 02:43 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 34 Votes on 26 Posts
Yes. Emphasis on minor....................
 
  #4  
Old 08-14-15, 03:30 PM
Z
Member
Thread Starter
Join Date: Oct 2013
Posts: 592
Received 0 Votes on 0 Posts
So they all get changed after a while? Like preventative maintence yearly tune up thing?

Reason I ask I see a bit of burn on the contacter pads on mine.... its been in service for 2 cooling seasons. Is that too soon to see signs of heat?
 
  #5  
Old 08-14-15, 04:01 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,496
Received 15 Votes on 10 Posts
You can replace the contactor if you feel the need, however it's not something that usually gets replaced unless it's causing a problem. My 25 year old system is still all original (capacitors and contactor).
 
  #6  
Old 08-14-15, 05:19 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 56,382
Received 747 Votes on 702 Posts
The contactors of 25 years ago will hold up better than today's as they were built much better.

A/C contactors used to be $35-$50. Now they're $10-$25.
 
  #7  
Old 08-14-15, 05:52 PM
Z
Member
Thread Starter
Join Date: Oct 2013
Posts: 592
Received 0 Votes on 0 Posts
Are they universal? When replacing one do I have to use the same part that came with the unit or can I use different one as long as the ratings match?

Are there better quality replacement contactors?
 
  #8  
Old 08-14-15, 08:05 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 34 Votes on 26 Posts
The ratings that are important are the coil voltage (almost always 24 volts AC but there are a few exceptions), the contact voltage which must be a minimum of 240 volts AC and the amperage rating which must be sufficient to handle the load of both the compressor and the fan motor together.

The voltage and amperage (often motor horsepower is listed in addition to amperage) MUST be at least the same as the original equipment but having higher ratings is allowable and may give longer life.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: