not sure I have a problem


  #1  
Old 08-18-15, 04:08 AM
F
Member
Thread Starter
Join Date: Aug 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
not sure I have a problem

Doing some cleaning on my a/c evaporator coil. I noticed that my coil appeared to only be wet about half way up. So I proceeded to check my superheat and subcool measurements. My subcool is about 10 degrees and my superheat about 3.5 degrees. I believe both should bee about ten degrees. The unit cools well with a difference of about 15 degrees between the intake and the output air. However the humiidty seems high in the house around 40%. I have a 2010 goodman 2.5 ton heatpump 15 seer. It uses 410a freon. Is there possibly a problem.
 

Last edited by ferdly; 08-18-15 at 05:52 AM.
  #2  
Old 08-18-15, 07:01 AM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,402
Upvotes: 0
Received 5 Upvotes on 5 Posts
40% RH is fine, but coil half way wet may be a problem, what type of metering device you have ? Is the large pipe ice cold ? (if you want me to guess----may be refrigerant a little low----, since you can check subcool or super heat, you should be able to check that out yourself, 15 degrees split is not great, but acceptable)
 
  #3  
Old 08-18-15, 07:03 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
The only thing that caught my eye is the SH and Delta T. Where did you take temp reading, inside or out?
 
  #4  
Old 08-18-15, 08:45 PM
F
Member
Thread Starter
Join Date: Aug 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
Outside, approximately 6 inches from service valve.
 
  #5  
Old 08-19-15, 06:40 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Take temp reading inside at the evap coil. See if you get a diff reading. TXV or piston?
 

Last edited by skaggsje; 08-19-15 at 06:41 AM. Reason: added
  #6  
Old 08-19-15, 07:14 AM
F
Member
Thread Starter
Join Date: Aug 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
TXV. You taliking about where the line goes out and into the coil correct.
 
  #7  
Old 08-19-15, 12:10 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Yes, on the suction line at the evap coil.
 
  #8  
Old 08-19-15, 07:22 PM
F
Member
Thread Starter
Join Date: Aug 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
temp on suction line 54 at the evaporator. temp of liquid line before txv is 87
 
  #9  
Old 08-21-15, 02:25 PM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,498
Received 66 Upvotes on 61 Posts
This is a forum for homeowner type repairs, not for refrigeration technicians.
In most areas you need to be certified/qualified to work on refrigeration sealed systems and is not an area these forums will help with.

It's expected that members who answer questions here will respect our rules.