Replacement R-22 condensor/compressor available?

Is it still possible to buy a replacement unit? The evaporator coil in the attic is only 5 years old and I'd rather not junk it. I'm in Houston.

Thanks
 
  #2  
Old 09-08-15, 05:36 PM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 19,281
Received 6 Upvotes on 6 Posts
I'm no expert, but I don't think there's any problem with R-22. AFAIK it's R-12 that has gone away.

Oops...no, just looked it up and I'm completely off. Was mixing my auto and residential.

What have you been told the problem is? Compressor failure? Or they just don't want to work on it?

I highly doubt you'll find an entire outside unit anymore, but a compressor itself may be available.

Though once you weigh all the factors (labor and refrigerant costs), it may be cheaper to replace with a new unit.
 
  #3  
Old 09-08-15, 05:45 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,471
Received 87 Upvotes on 80 Posts
http://www.amazon.com/s/ref=nb_sb_no...+condenser+dry

It is still possible to by R22 condensers that are shipped with no refrigerant ( dry units).

A better option might be to replace the expansion valve in your evaporator coil, blow out the piping with nitrogen and buy a R410 condenser.
 
  #4  
Old 09-08-15, 05:45 PM
G
Member
Join Date: Nov 2011
Location: USA
Posts: 593
Upvotes: 0
Received 2 Upvotes on 2 Posts
Still have nitrogen filled condenser here.I slowed way down and still helped with maybe three this summer.
 
  #5  
Old 09-09-15, 04:59 AM
I
Member
Thread Starter
Join Date: Mar 2007
Location: Jupiter
Posts: 161
Received 0 Upvotes on 0 Posts
Thanks Folks,
I think the a/c guy has managed to breathe life into the old beast for now. But major question…..can I retrofit a new modern (non R-22) compressor and mate it with the (R-22) evap coil? That would be great if I could do that.
Very strange problem, unit would not get temp below 80F, compressor running constantly. Freon good, evap coil clean, but very hot here in Houston, plus we had to turn off the downstairs unit for 3 days due to some construction work. The upstairs unit was working hard, probably too hard for its 23 years. He blasted the condenser coil with water, had the gauges connected and showed me the relationships between the input and output pressures and cleaning the coil got us back into an acceptable range on both gauges. She’s running fine at moment, temp is 77, which is where we keep it anyway. We’ll see how it goes. Just thinking about replacement options, was think R-22 unit, but now reading that R-22gas will be costly due to import bans coming into effect on new R-22, so only reclaimed will be available for maintenance.
 
  #6  
Old 09-09-15, 07:22 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
If strait A/C use Retro R-22 replacement R-422D; if heat pump &/or A/C use R-438A.
Not high Dollar, & both work okay in every way; contractors can get those refrigerants for your system.
 
  #7  
Old 09-09-15, 09:37 AM
I
Member
Thread Starter
Join Date: Mar 2007
Location: Jupiter
Posts: 161
Received 0 Upvotes on 0 Posts
Thanks, so if I'm understanding correctly, if it comes to it I could get eg: a Goodmans R-22 and fill it with R-422D? All seems good so far with the old unit but we'll see, I think I overheated the old girl......similar to the effect I used to have on the better half.
 
  #8  
Old 09-09-15, 11:58 AM
T
Member
Join Date: Dec 2005
Location: USA
Posts: 173
Upvotes: 0
Received 0 Upvotes on 0 Posts
I've used the replacement refrigerants such as 422B and 422D. I was not happy with the results. Often times I lost enough capacity that the unit would not cool on hot days. For me its either real R22 or nothing.
 
  #9  
Old 09-09-15, 01:16 PM
I
Member
Thread Starter
Join Date: Mar 2007
Location: Jupiter
Posts: 161
Received 0 Upvotes on 0 Posts
Got it thanks. yep I'm seeing mixed reviews on the 422 product. You Tube has some positive videos, but am seeing reviews that are negative also. I'll proceed with caution, hopefully the original unit will keep going, but I may have to get a complete new system when the old workhorse finally croaks. We are into the afternoon here and she hasn't missed a beat so far. I honestly thought I was in for a new unit yesterday so was well pleased with the A/C guys check that Freon was full on both units and the $50 bill for his coil cleaning work and gauge test on both a/c's.
 
  #10  
Old 09-12-15, 06:43 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
Unless the companies are misrepresenting their tests, Both R-438A (I trust DuPont) for both heat pumps & A/Cs & R-422D on A/Cs only should be okay.

There re z lot of reasons that the new refrigerant can get blamed for the unit not keeping up. It may not have kept-up with R-22 either.
 
  #11  
Old 09-12-15, 09:36 PM
T
Member
Join Date: Dec 2005
Location: USA
Posts: 173
Upvotes: 0
Received 0 Upvotes on 0 Posts
A lot of irresponsibe information being put out there to the general public on this thread.

Even the manufacturer of 422D says it should only be used for low or med temperature refrigeration. Not home air conditioning.

And they all are rated at up to 10% less capacity than R22. I've personally seen this reduction if not worse. Buyer bewared if someone wants to put these replacements in your system.

Here is one of many links that spells it out.

http://www.refrigerants.com/pdf/R422D_LINK.pdf
 
  #12  
Old 09-17-15, 05:23 AM
W
Member
Join Date: Jan 2014
Location: USA
Posts: 630
Upvotes: 0
Received 0 Upvotes on 0 Posts
R22 , brand new / virgin refrigerant is certainly available . It is not cheap , but it is no where near as costly as some HVAC people would have you believe .

If the old condenser / compressor is bad , I would seriously consider a new , dry charged R22 replacement condenser .

If your existing system is not a burn out or in some other way contaminated , I would think the R22 could be used to ( at least partially ) charge a new dry charge unit ?

God bless
Wyr
 
  #13  
Old 09-27-15, 06:28 AM
B
Member
Join Date: Mar 2015
Location: Canada
Posts: 179
Received 1 Upvote on 1 Post
Thanks Folks,
I think the a/c guy has managed to breathe life into the old beast for now. But major question…..can I retrofit a new modern (non R-22) compressor and mate it with the (R-22) evap coil? That would be great if I could do that.
It's really not worth it to screw around with something which may or may not work when the price of an entire new system is as cheap as it is. You don't mention your ac size but you can get a complete goodman precharged (r410a) 3 ton ac unit with coil starting around $1000. The retrofit you're talking about including the r22 charge is at least that much..... probably more
 
  #14  
Old 04-27-16, 10:03 AM
I
Member
Thread Starter
Join Date: Mar 2007
Location: Jupiter
Posts: 161
Received 0 Upvotes on 0 Posts
I think she's on the way out

Well we are not into May yet and she looks to be struggling. I think it's a 3 ton. Has there been any developments around using R410A in systems that ran R-22 or is it a total system swap?
Thanks
 
  #15  
Old 04-27-16, 08:17 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,053
Received 3,593 Upvotes on 3,222 Posts
Didn't we already address this question.

You're in an area that relies on A/C..... replace the condensor and the evaporator as a matched set.
 
  #16  
Old 04-29-16, 01:53 PM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,491
Upvotes: 0
Received 8 Upvotes on 8 Posts
100% agree with PJmax! wasting your money on a un-matched system
 
  #17  
Old 04-30-16, 08:32 AM
I
Member
Thread Starter
Join Date: Mar 2007
Location: Jupiter
Posts: 161
Received 0 Upvotes on 0 Posts
OK thanks for the updates.
 
 