Air handler runs all the time in heat normal in cool.

Hey folks, first thanks in advance for this great resource for help. I have a Goodman air handler ASPF426016BA and a sensi thermostat. In heat mode it runs the fan in the air handler all the time, does not shut off unless i throw the breaker, in cool it works fine, you can hear the thermostat working however the handler is being disobedient. Any advice is appreciated.
Thanks
Jet
 
  #2  
Old 02-12-16, 01:54 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 2,101
Received 0 Votes on 0 Posts
Is this a heat pump system?
 
  #3  
Old 02-12-16, 04:28 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,183
Received 1,528 Votes on 1,411 Posts
Welcome to the forums.

Can't tell if heat pump by the air handler model. Shows use as heat pump or A/C only.

It sounds like the wire that should be on G is on O/B.
 
  #4  
Old 02-18-16, 10:37 PM
J
Member
Thread Starter
Join Date: Feb 2016
Location: United States
Posts: 2
Received 0 Votes on 0 Posts
Guys I,have a Sensa thermostat on it I'm not happy with it so I'm putting a different thermostat on it tomorrow."
 
 