A/C fan turns but compressor won't turn over
Old 03-15-16, 04:27 PM
Need help my compressor will not turn over I just put in a new capacitor and nothing happens it seems like it wants to start but it just gives out.... Any ideas or suggestions..
Thanks😞
Old 03-15-16, 06:39 PM
Houston204's Avatar
Received 17 Votes on 14 Posts
Is the compressor hot? The compressor can shut off on thermal protection if you had a cooling demand present with a bad capacitor.
If the stat was off for a few hours before you replaced the cap it is probably something else.
The wire connections to the compressor might need to be inspected.
Name:  Compressor terminals.jpg
A wire connector may require replacement.
Name:  compressor terminal damage.jpg
There are kits available for this repair.
Safety glasses should be worn and power should be removed before inspecting the compressor terminals.
Old 03-15-16, 06:47 PM
Houston204's Avatar
If you have a multimeter you can take some Ohm readings from the control box end of the compressor wires to see if the wiring is okay.
This is safer since the compressor terminals have 150 to 220 psi of pressurized refrigerant and can blow out if they are damaged.
Old 03-15-16, 08:15 PM
Houston204's Avatar
Posting the make and model along with the microfarad rating of the new capacitor might be of assistance.
Old 03-26-16, 05:34 PM
C
In this case, how would we know if the compressor has seized?
Maybe that is the issue?
Old 03-26-16, 06:53 PM
Received 1,173 Votes on 1,088 Posts
You won't know until you've checked everything out.
The wiring needs to be confirmed that all three connections are on the compressor.
The windings need to be checked for proper continuity.
The cap wiring needs to be double checked.
If all checks out good.... suspect a defective compressor.
As one last resort you could try a hard start kit on the compressor.