Condenser problems, fan won't start.


  #1  
Old 05-03-16, 07:27 PM
L
Member
Thread Starter
Join Date: May 2016
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Condenser problems, fan won't start.

So I came home a couple days ago and it was 82 degrees inside. I tried turning the ac system off and on but the condenser would not start at all, I checked on it and it was pretty hot. I have been looking online for remedies and I have tried a couple. First I re-wired the fan motor separately to 220V and it worked fine. Next the capacitor was definitely shot, bulging and had no ohms when tested. So I bought and installed everything back. Turned everything on and was feeling hopeful when the compressor kicked on, I waited but the fan never started.
It is now 85 degrees and I'm losing hope. I might have to bite the bullet and call out a technician. I would greatly appreciate anyone out there that has any advise, or would help me troubleshoot through steps.
 
  #2  
Old 05-03-16, 07:58 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,539
Received 38 Votes on 34 Posts
What is the make and model of this unit?

Did you install a dual capacitor?

Posting some pictures of your wiring may allow us to offer better assistance.
 
  #3  
Old 05-04-16, 03:20 PM
L
Member
Thread Starter
Join Date: May 2016
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Here are a couple pics that will answer your questions.



 

Last edited by LouisBMG21; 05-04-16 at 03:39 PM.
  #4  
Old 05-04-16, 03:23 PM
L
Member
Thread Starter
Join Date: May 2016
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
And yes, I replaced the capacitor with exactly the same thing. 35/5 uF 370V
 
  #5  
Old 05-04-16, 05:00 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,539
Received 38 Votes on 34 Posts
I suspect that common and run are reversed.
I see the way the diagram has the wiring. Can we see the actual wire connections?
 
  #6  
Old 05-04-16, 05:13 PM
L
Member
Thread Starter
Join Date: May 2016
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Yes of course

and the black is connected to the contactor
 
  #7  
Old 05-04-16, 09:35 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 70,190
Received 2,982 Votes on 2,690 Posts
That capacitor is wired correctly according to the diagram.

The black wire from the fan motor goes to the opposite side (T2) of the contactor as the yellow wire (T1) to the capacitor.
 
 