1 year old A/C condensor not turning on


  #1  
Old 05-06-16, 11:28 AM
T
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
1 year old A/C condensor not turning on

Hi,

I have a 1 year old Tempstar AC/Heat unit. Heater works fine.

Only when I turn on AC, the fan and compressor outside don't go on.

AC technician stopped by and replaced capacitor and fuses. And said that AC breaker is only reading 94 volt, once I replace it, AC will work.

I replaced the breaker. Now there is 134 volt power to AC unit.

Still same thing, when I turn on AC, the fan and compressor outside doesn't go on.

I already called AC technician to come out again, but it won't be for few days. Any suggestions, I want to have second opinion before AC technician is out here.

Thanks,

Paul
 
Attached Images    
  #2  
Old 05-06-16, 12:22 PM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,406
Upvotes: 0
Received 6 Upvotes on 6 Posts
You can push the contactor button(use an insulated stick) to see if that turn it on. The contactor is that small black box right next to the capacitor (see the second photo). there is a small button in the middle of it (see through the yellow curved wire location in the photo)
 
  #3  
Old 05-06-16, 12:56 PM
T
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
I pressed the button down at contactor. Nothing happens with AC fan or compressor.

Thanks,

Paul
 
Attached Images  
  #4  
Old 05-06-16, 01:47 PM
T
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
I just found out the everytime I press the contact button, AC breaker(50amp) trips.

This is why my AC is not coming out.

I have already replaced the breaker.

Is there anything else can caused AC breaker(50amp) to trip.

Thanks,

Paul
 
  #5  
Old 05-06-16, 02:03 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,471
Received 87 Upvotes on 80 Posts
The two most common causes for your symptoms are a wire has rubbed against a copper pipe in the unit and created a short, or the compressor has shorted to ground internally.
 
  #6  
Old 05-06-16, 03:00 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,606
Received 71 Upvotes on 62 Posts
It's possible that you have a shorted compressor winding, or the winding is shorted to ground. You would have to turn off the power to the outdoor unit, and disconnect the wires where they connect to the compressor (usually 3 wires). You should wear protective eyewear before removing the compressor wires, as the compressor is under pressure, and there's always a chance that the pressure could release while working on it.

With the wires disconnected from the compressor, measure the resistance between each of the terminals. Assuming 3 terminals (1, 2, 3), you would measure resistance between 1-2, 2-3, 1-3. The resistance is typically something similar to what's shown below.

Pin 1 to Pin 2 – 3 ohms
Pin 2 to Pin 3 – 6 ohms
Pin 1 to Pin 3 – 9 ohms

Also, check resistance from all the compressor terminals to the chassis (ground) on a high ohms scale. You should measure infinite resistance (should measure as an open circuit).
 
  #7  
Old 05-06-16, 05:24 PM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,406
Upvotes: 0
Received 6 Upvotes on 6 Posts
If you don't have a meter or don't want to measure the ohms as suggested, you can try to disconnect compressor, then push the button, and connect it back but disconnect the fan then push the button. By doing this simple test, you should be able to find out which one is shorted. (but be careful, 240V down there !)
 
  #8  
Old 05-06-16, 05:56 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,063
Received 3,596 Upvotes on 3,225 Posts
It maybe best not to try the disconnect and repower method of troubleshooting or that contactor may explode.
 
  #9  
Old 05-06-16, 09:12 PM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,406
Upvotes: 0
Received 6 Upvotes on 6 Posts
Well, up to him, but I have never had a contactor explode on me.
 
  #10  
Old 05-07-16, 09:54 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,014
Received 158 Upvotes on 144 Posts
If you feel comfortable working inside the unit,with the power OFF remove the 2 wires from the contractor that go to the compressor,restore the power and with someone inside have them turn the thermostat for a call for cooling and see what happens.
 
  #11  
Old 05-07-16, 04:52 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,471
Received 87 Upvotes on 80 Posts
The 2 wires on the contactor are Run and Common. There will be a third wire feeding Start. It is the blue wire on the C terminal of the run capacitor.
 
  #12  
Old 05-09-16, 08:46 AM
T
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you and will update

Busy with Mother's day weekend.

Thank you for these information, but I don't have any help so I will leave your suggestions for AC technician which will come out for free the second time.

Thank you again and will update you the result.

Paul
 
 