A/C condensor won't turn on
Old 10-02-16, 08:45 AM
I turn the breaker on and off.
We had an issue with our compressor and fan last month where they wouldn't turn on. I changed out the capacitor thinking they wouldn't both go out at the same time. Everything worked.
Then, today the same thing. I thought it was odd that another capacitor would go out so quickly. So I tested flipping the breaker off, then back on. After a 5 minute short cycle it kicked back on.
Any ideas why it would suddenly start doing this?
Thanks,
David
Old 10-02-16, 10:25 AM
Is the breaker tripping? Let us know.
Old 10-02-16, 11:03 AM
No it does not flip. It just happened again that it won't turn on. This time flipping it manually did not work. I wonder why changing the capacitor previously "fixed" it for about a month. There has to be an underlying cause.
Old 10-02-16, 01:05 PM
the compressor could be going off on internal overloads. Which means its getting to hot. Could be low on refrigerant.
Old 10-02-16, 01:38 PM
I'll look into that. The only thing I question about that is the fan and compressor are on different capacitors. Wouldn't the fan turn on still?
Old 10-02-16, 02:43 PM
Received 3,951 Upvotes on 3,544 Posts
You're guessing at the problem.
You need to confirm that the contactor IS actually closing and the fan and compressor aren't working. It sounds like more to me a defective/corroded contactor.
I would check for 240v at the incoming line side of the contactor and then again on the outgoing side.
Old 10-02-16, 03:57 PM
Thanks. It's pouring right now, but I will check that next.