A/C wont turn on unless I hold contactor in


  #1  
Old 05-25-16, 07:29 PM
B
Member
Thread Starter
Join Date: May 2016
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
A/C wont turn on unless I hold contactor in

My ac will not start when i turn the thermostat on. But it will turn on if i hold down the the pole on the contactor and it runs just fine, but i have to hold it down. I also do have a brand new furnace 4 moths old. Any help would be great thank you
 
  #2  
Old 05-25-16, 11:19 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Welcome to the forums.

Has the A/C ever worked since the new furnace was installed ?
Do you have a voltmeter ?

There are two wires in a cable going to outside unit. Those two wires need to be checked for 24vac when system is calling for cool. You can check them where they splice in near the electrical connection area.

Keep in mind that there is a five minute (maybe more) of a delay when the stat calls for cooling before the compressor starts up.
 
  #3  
Old 05-26-16, 05:01 AM
B
Member
Thread Starter
Join Date: May 2016
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
I never tested ac after furnace got replace cause it was winter. And i will get voltmeter after work today test the volts.
 
  #4  
Old 05-26-16, 10:51 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Since you just had the furnace installed less then four months ago... you can also check with the installer too for repair help.
 
  #5  
Old 05-26-16, 03:45 PM
B
Member
Thread Starter
Join Date: May 2016
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
SO i used the voltmeter and it looks like im not getting 24volts to the contactor. SO would that be the wiring inside the house then?
 
  #6  
Old 05-26-16, 03:59 PM
F
Member
Join Date: Nov 2015
Location: USA
Posts: 21
Upvotes: 0
Received 0 Upvotes on 0 Posts
There is a transformer that supplies the 24v. You need to check if that is burned out. If it is not then you need to check your thermostat to make sure that it is relaying the 24v when calling for cool.
 
  #7  
Old 05-26-16, 04:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Ok.... if you select FAN ON..... does the inside blower work ? If yes.... the transformer is good.

I'm pretty certain your system may be low on refrigerant. You measured at the contactor and did not find 24vac.

Now measure where the wires connect to the unit from the house with wire nuts. This will confirm if the problem is inside or outside.
 
  #8  
Old 05-26-16, 06:30 PM
Former Member's Avatar
Member
Join Date: May 2006
Location: US
Posts: 726
Upvotes: 0
Received 0 Upvotes on 0 Posts
not sure what you have there but if it is an attic air handler it might be as simple as the float switch in the drain pan not installed correctly. I have heard that some installers get in a hurry and do not do a proper startup check. They could have left the switch laying loose in the pan wedged against the side or something LOL.
 
 