AC furnace blower kick on and off after 5s
#1
Member
Thread Starter
Join Date: May 2016
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
AC furnace blower kick on and off after 5s
I have a goodman awb24-08d furnace.The furnace has been working fine all winter. I recently turned on the A/c for the summer but the fan kicked on for 5s then kick off.I then went to the thermostat and try to manually turn on the fan but the Auto/on switch kick the fan on for 5s then off.If I turn the heat on the fan works perfectly.I just replaced the board control and blower capacitor.I have some pics.In the pic i disconnected NO and NC wire for test.Can anyone help?
http://imgur.com/a/sumPO
http://imgur.com/a/sumPO
#2
You may have a bad blower motor. Generally, the blower runs at a different speed for heating and cooling. It's possible that the winding for the cooling speed is bad (probably shorted).
#3
Member
As you can see in the wiring diagram in heat mode the fan is started by the heat sequencer and in cooling mode the stat starts the blower. Do you have a voltmeter?
#5
Member
Set your stat to call for cooling and put your meter on G and C on the broad. You should have 24 volts.