A/C condensor and coil
Is installing a 4 ton condenser and a 3 1/2 ton coil a good idea? (I hope I got that right on the part names)
#2
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 37 Upvotes
on
29 Posts
No. Sometimes a slightly larger evaporator (about a 1/2 ton) is used for improved humidity control but never a larger condensing unit. In other words, a 4-1/2 ton evaporator would be okay for the four ton condenser but never the other way around.