A/C condensor and coil

Is installing a 4 ton condenser and a 3 1/2 ton coil a good idea? (I hope I got that right on the part names)
 
  #2  
Old 06-17-16, 03:33 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 37 Upvotes on 29 Posts
No. Sometimes a slightly larger evaporator (about a 1/2 ton) is used for improved humidity control but never a larger condensing unit. In other words, a 4-1/2 ton evaporator would be okay for the four ton condenser but never the other way around.
 
 