Goodman central air condensor wont turn on
#1
Goodman central air condensor wont turn on
Neither cond or fan turns on outside Goodman unit, checked breaker panel,
thermostat, & condensation unit.
There is 20v going to the fan motor to the outside, looks like the cap is inside the motor, tried spinning the fan manually, wont kick in.
thermostat, & condensation unit.
There is 20v going to the fan motor to the outside, looks like the cap is inside the motor, tried spinning the fan manually, wont kick in.
#2
checked breaker panel
#4
Clocert, where would the contactor be on mine?
https://www.dropbox.com/sh/es52l9rin...E-5eEWsla?dl=0
And where would the reset but be?
https://www.dropbox.com/sh/es52l9rin...E-5eEWsla?dl=0
And where would the reset but be?
#5
Mid 2/3 to the right, that old relay with the big yellow wire attached to, should be the contactor. I can't not tell from the picture where the button is, usually right on the top. The relay should have 2 small wires attached to it. use an insulated stick push the button and see if that start the unit. This only test the contactor to see if you have 24V problem or contactor problem, not reset your condenser.
#6
Clocert, I think mine does not have a reset button. I looked an looked on the fan motor, compressor, etc... I did not set it.
I think the relay contactor should be fine since I replaced that about 10 years ago. But I will try your suggestion just to make sure. Thank you.
I think the relay contactor should be fine since I replaced that about 10 years ago. But I will try your suggestion just to make sure. Thank you.
#7
wrdiy..... you've got your problems spread out in several different threads. We try not to hijack threads as the answers get confusing.
No one said reset button. There is a place you push the contactor in.
In the picture of your contactor..... in the red box is the place where you push the contactor in to manually operate it. Use something non conductive like a stick.
Also....in the pink circle is what looks like an extremely burned contact. Based on what I see in the picture.... I'd change the contactor too.
No one said reset button. There is a place you push the contactor in.
In the picture of your contactor..... in the red box is the place where you push the contactor in to manually operate it. Use something non conductive like a stick.
Also....in the pink circle is what looks like an extremely burned contact. Based on what I see in the picture.... I'd change the contactor too.

#8
Originally Posted by PJMax
wrdiy..... you've got your problems spread out in several different threads. We try not to hijack threads as the answers get confusing.
Clocert did not say reset button in this thread but in another thread and I was trying to consolidate those questions. Yeah, not my usual practice of HiJack.

Anyway, thanks for pointing out about the contactor and take the time to circle in the picture.
#9
Correction: New Capacitor, wont turn on, 120 on cap & relay, 240 on breaker box
New capacitor, read 120 on cap, 240 on outside breaker box, no action from fan or condensor
#10
Problem solved: contactor spring would not lock in on relay
I made a long stiff wood slat out of a shim, & pushed in the spring, & the fan & condensor started up, would stop when let go, going to order new relay.