Disconnect for A/C condensor unit

Hi guys,

I'm installing a Pioneer split type air conditioner (WYE018GMFI15RL):
Power source: 208-230V~ 60Hz, 1Ph
Minimum circuit ampacity: 14A
Max. Fuse: 20A

I've installed the 220 circuit on a 20A double breaker and this leads to the exterior GE 30 Amps disconnect (model TF30R). The disconnect needs 2 fuses in the handle. Fuses allowed are H, K1, K5, K9, RK1, RK5.

The Big Question: What AMP size fuses should I use? 2x 20A or 2x 10A


The Small Question: Will any of the mentioned classes suffice (H, K1, K5, K9, RK1, RK5)?

I appreciate your help!
 
Sponsored Links
  #2  
Old 09-01-16, 01:27 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 2,101
Received 0 Votes on 0 Posts
You could just leave the 30A fuses in there.
 
  #3  
Old 09-01-16, 01:36 PM
O
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 30
Received 0 Votes on 0 Posts
There are no fuses in the handle right now so there's nothing to leave there.

Also, 30A fuses would exceed the 20A max fuse limit, wouldn't it?
 
  #4  
Old 09-01-16, 01:54 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 35 Votes on 27 Posts
Since minimum circuit Ampacity is 14 amperes you cannot use a 10 ampere fuse. I would use the smallest slow-blow fuse, starting with 15 ampere, that will allow the unit to start reliably, not going over 20 ampere.
 
  #5  
Old 09-01-16, 02:09 PM
O
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 30
Received 0 Votes on 0 Posts
Okay! I was asking because two (hot) 110v lines go into the disconnect and I didn't know if you add up the two fuses that are used. Following your advice I will start with two 15 amp fuses. Thanks!
 
  #6  
Old 09-01-16, 02:49 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Just for the record you have 240v not 220v. There are no 110 lines running to the disconnect. There are the two 240 volt legs of the power supplied to your house running to the disconnect.
 
  #7  
Old 09-01-16, 03:39 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,150
Received 1,113 Votes on 1,033 Posts
I would use 15A fuses.

You should have installed a 30A or 60A non-fused disconnect as the circuit is protected by the 20A circuit breaker.
 
  #8  
Old 09-01-16, 07:13 PM
O
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 30
Received 0 Votes on 0 Posts
Thanks for the 'record' Ray2047. So if I would measure one leg it would read 240v?
 
  #9  
Old 09-01-16, 07:26 PM
O
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 30
Received 0 Votes on 0 Posts
I'll use 15A fuses. But why should I have used a non-fused disconnect as you suggest?
 
  #10  
Old 09-01-16, 08:03 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,150
Received 1,113 Votes on 1,033 Posts
The two pole 20A breaker is all your unit requires for protection. You are double protecting your unit. It won't hurt anything it's just not required or necessary.

The only place you'd have to use a fused disconnect is if you had an existing 30A circuit and you needed to protect your A/C at a lower current.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: