3A fuse blows on control board

Reply

  #1  
Old 10-09-16, 05:13 PM
Member
Thread Starter
Join Date: Oct 2016
Posts: 2
Received 0 Votes on 0 Posts
3A fuse blows on control board

Okay so I've read all the threads I can find...contactor and 4 way valve unplugged. I can't find any wires degraded, replaced air handler fan capacitor, still blowing fuses. I've got 28v out of the transformer 248 in. Red blue and white wires have continuity at the thermostat...Name:  VZM.IMG_20161009_125545.jpg
Views: 229
Size:  18.0 KB
 
Sponsored Links
  #2  
Old 10-09-16, 05:31 PM
Member
Join Date: May 2015
Location: USA
Posts: 3,138
Received 1 Vote on 1 Post
Tell us make and model of your equipment, please.
When does the fuse blow, as soon as you apply power to equipment? When thermostat calls for heat/cool? A more detailed explanation would help us help you.
 
  #3  
Old 10-09-16, 07:05 PM
Member
Thread Starter
Join Date: Oct 2016
Posts: 2
Received 0 Votes on 0 Posts
I found it lol! The stupid overflow shutoff switch was shorted! Thanks for looking everyone.
 