Blower unit hums faintly when off


  #1  
Old 12-20-16, 05:23 PM
I
Member
Thread Starter
Join Date: Jan 2013
Location: US
Posts: 115
Received 1 Upvote on 1 Post
Blower unit hums faintly when off

My blower unit is in the attic.

During the Summer, the central A/C unit worked perfectly. Now, I switch to Heat in Auto mode, it will not turn on. But if switch to ON, the blower unit kicks in but no heat, temperature intake=outtake.

At the thermostat (Hunter), if I turn it OFF, the blower unit faintly hums. When I go back in the attic, what should I look for?

Thanks.

Name:  blower model.jpg
Views: 352
Size:  51.8 KBName:  Thermostat.jpg
Views: 324
Size:  43.6 KBName:  blower unit.jpg
Views: 313
Size:  24.7 KB
 
  #2  
Old 12-21-16, 05:52 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
That's an electric furnace so when the stat is set to auto the heat and blower are started by the sequencer. If you have a meter test between W and common to see if the stat is sending 24vac.

BTW, the installer should be slapped for running the cables and high voltage wires right in front of the access door.
 

Last edited by skaggsje; 12-21-16 at 05:56 AM. Reason: added
  #3  
Old 12-23-16, 02:57 PM
I
Member
Thread Starter
Join Date: Jan 2013
Location: US
Posts: 115
Received 1 Upvote on 1 Post
I've measured RC to W/B and RC to Y/O (photo), and both shows 29.5VAC. When measured G to RC, it shows 29VAC. Everything else shows .5VAC or less (G-W/O, G-W/B
 
Attached Images   
  #4  
Old 12-23-16, 03:14 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,752
Received 673 Upvotes on 571 Posts
if I turn it OFF, the blower unit faintly hums
The hum you are hearing is likely nothing but the control transformer and is nothing to worry about. It converts 120 volts to 24 volts for the stat.
 
  #5  
Old 12-23-16, 03:29 PM
I
Member
Thread Starter
Join Date: Jan 2013
Location: US
Posts: 115
Received 1 Upvote on 1 Post
I din't think about that transformer constantly converting... Good to know. What else should I check next for no heat/blower? Thanks.
 
  #6  
Old 12-23-16, 05:10 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,752
Received 673 Upvotes on 571 Posts
Have you tried new batteries in the stat?

If this is an electric furnace, are the breakers on for the heat strips?
 
  #7  
Old 12-24-16, 07:49 AM
I
Member
Thread Starter
Join Date: Jan 2013
Location: US
Posts: 115
Received 1 Upvote on 1 Post
When I removed the thermostat, the LCD stayed on while I was testing, so I'm guessing the batteries are good. But I'll test the battery when I get there this morning.

Are you talking about that 2 breaker switches on the front of the blower unit? Yes, they were both on when I was testing, although the photo shows off.

I'll check the limit switch today.

Also, according to the manual, RH is also 24V, but it's not connected. Does it need to be jumper to RC? According to the manual RC and RH should be jumpered if there is no RH wire. And the brown wire wasn't hooked up, I'm guessing it's a spare.


Name:  blower unit.jpg
Views: 226
Size:  25.4 KBName:  blower switch.jpg
Views: 179
Size:  40.8 KBName:  theromstat wiring.jpg
Views: 229
Size:  34.2 KB
 

Last edited by itchibahn; 12-24-16 at 08:39 AM.
  #8  
Old 12-24-16, 10:33 AM
I
Member
Thread Starter
Join Date: Jan 2013
Location: US
Posts: 115
Received 1 Upvote on 1 Post
Resolved....

I put a jumper between the RC and RH, and all working like it should.

I don't understand why the jumper was missing to start with. I had my AC guy check it out when I bought this house earlier this year. I'm wondering, because I had to call him twice a year when season changes on all both of my houses....

Thanks for all your help. I just saved $125 trip charge.
 
  #9  
Old 12-24-16, 10:43 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,017
Received 3,407 Upvotes on 3,057 Posts
Talk about psychic..... I saw your wiring on the stat and was just typing my reply.

Good find.
 
  #10  
Old 12-25-16, 06:13 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,752
Received 673 Upvotes on 571 Posts
According to your picture of the breakers, they are in the off position. They should be on for electric heat strips. Perhaps there is a heat pump?

I'm wondering, because I had to call him twice a year when season changes on all both of my house
He would just move the red wire from RH to RC, or vice versa, depending on the season. That sounds like a scam to get you to call for service.
 
 